You need to know the conductivity of the armour not what it's copper equivalent is and I suspect this is where it is going wrong.
I believe the calculations that the figures I have mentioned have been calculated using the K factors.
 
GN8 advices on factors to be used when the material for the main protective bonding is not copper so it's conductivity can be calculated. This will apply in the OPs case as the armour is being used to support the bonding.
 
GN8 advices on factors to be used when the material for the main protective bonding is not copper so it's conductivity can be calculated. This will apply in the OPs case as the armour is being used to support the bonding.
The conductivity has been factored in, I thought we were trying to ascertain if the armour was large enough to cater, for both the main earth, and the main bonding conductor. in this case it clearly is not suitable size wise, which incidentally makes a mockery of what the scam has told the OP.
 
The coefficient restivity of copper at 20 degree C is 0.004, the restivity of steel changes with carbon content hence the guidance in GN8. I believe GN8 gives a ratio of 1:8.5. So If 10mm copper is deemed adequate as the CSA of a bonding conductor but you want to use the Steel armour as the bonding conductor or forming part of a bonding conductor then you need to apply the ratio that's provided in GN8.

10mmx8.5=85mm

The CSA of 35mm 4core XLPE armoured cable is 78mm

78mm is smaller than the required 85mm.

As its smaller than the required CSA it's not deemed adequate to use as or form part of a bonding conductor.
 
ok so you guys have put the case forward that the Nic must have got it wrong , and to be honest after reading your facts and calculations i think you must be right !
so going to tell builder get the block paving up again /dig out the trench and we will install the earth
better to be safe than sorry!
 
ok so you guys have put the case forward that the Nic must have got it wrong , and to be honest after reading your facts and calculations i think you must be right !
so going to tell builder get the block paving up again /dig out the trench and we will install the earth
better to be safe than sorry!
dont tell the builder, just show up with a sledgie and start battering the slabs.

you could also run an overhead with a steel support cable, i imagine theres going to be an argument when you ask him to lift all the slabs.

why cant you just drive an earth spike into the ground with a decent CPC? seems easier than lifting 35metres worth of slabs and digging a trench
 

Reply to PME head , builder forgot earth cable , 100amp 3phase supply , 10 bedroom house , 10 bedroom house in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top