Table 5 OSG I thinkYou need to know the conductivity of the armour not what it's copper equivalent is and I suspect this is where it is going wrong.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss PME head , builder forgot earth cable , 100amp 3phase supply , 10 bedroom house , 10 bedroom house in the The Welcome Forum area at ElectriciansForums.net
Table 5 OSG I thinkYou need to know the conductivity of the armour not what it's copper equivalent is and I suspect this is where it is going wrong.
I believe the calculations that the figures I have mentioned have been calculated using the K factors.You need to know the conductivity of the armour not what it's copper equivalent is and I suspect this is where it is going wrong.
The conductivity has been factored in, I thought we were trying to ascertain if the armour was large enough to cater, for both the main earth, and the main bonding conductor. in this case it clearly is not suitable size wise, which incidentally makes a mockery of what the scam has told the OP.GN8 advices on factors to be used when the material for the main protective bonding is not copper so it's conductivity can be calculated. This will apply in the OPs case as the armour is being used to support the bonding.
dont tell the builder, just show up with a sledgie and start battering the slabs.ok so you guys have put the case forward that the Nic must have got it wrong , and to be honest after reading your facts and calculations i think you must be right !
so going to tell builder get the block paving up again /dig out the trench and we will install the earth
better to be safe than sorry!
Don't you mean EC?... with a decent CPC?
may as well use it as a back up anyways since its thereWhether he digs a new trench or employs TT, the main thing is that he is no longer relying on the armour.
probably, as its really not a circuit, i really should learn to read my own posts before i hit send.Don't you mean EC?