Pme not | Page 2 | on ElectriciansForums
Guest viewing is limited
Discuss Pme not in the UK Electrical Forum area at ElectriciansForums.net
G
Guest111
went to do some work for a relative today,change CU and a few odds and ends in a small shop which they have just rented,the landlord is a distant relative of theirs and has said they can do what they want.Anyway I was doing a few tests and found that the Zs on a radial was 400 ohms,Disconnected earth bonds at CU and tried to do a Ze,tester went into lockout straight away,anyway tested phase to neutral at cutout and got 240v tested phase to earth and nothing,it was a PME system so something very wrong. Anyway puts a call in to networks and about 2 hours later a guy came out and I explained the problem,he opened up the service head to find that a link had not been fitted between the neutral and earth,this was from 20 years ago when the new cable was fitted.He was not happy and neither was I it proves that not only was it not tested by networks when it was fitted,but obviously it has never been tested since,if this isnt a good advert for regular I&T then I don't know what is.
Reply to Pme not in the UK Electrical Forum area at ElectriciansForums.net
And exciting when that Hager AFDD finally tripped 😂
nicebutdim
N
It's not uncommon to find the earth cable put out from the additional neutral knockout, not the designed one on the side. If the rest of it looks...
Recommended Sponsor News
Hi everyone,