I'm not sure that it is an acceptable method of measuring Ra, because it does not measure Ra, it measures the earth loop impedance including the earth electrode.

Either way I didn't suggest that it was not an acceptable test method, I asked if this method had been used or if a better method had been used.
If he's made one end tt and disconnected the supply earth then yes he is measuring Ra

That's if he's disconnected it from the pme earthing
 
If he's made one end tt and disconnected the supply earth then yes he is measuring Ra

That's if he's disconnected it from the pme earthing

No, with a loop impedance tester he will be measuring the combination of Ra and the loop,impedance of the supply.
Ra is the resistance to earth of the earth electrode, it does not include the line conductor.
 
No, with a loop impedance tester he will be measuring the combination of Ra and the loop,impedance of the supply.
Ra is the resistance to earth of the earth electrode, it does not include the line conductor.
The earth fault loop impedance tester is connected between line conductor at the source of the installation (not in this case) and the earth electrode, and a test performed.
The impedance reading taken is treated as the electrode resistance.

Taken from GN3
So yes not as accurate as an electrode tester but is the method we can use to obtain Ra
 
The earth fault loop impedance tester is connected between line conductor at the source of the installation (not in this case) and the earth electrode, and a test performed.
The impedance reading taken is treated as the electrode resistance.

Taken from GN3
So yes not as accurate as an electrode tester but is the method we can use to obtain Ra

You are contradicting yourself.
You say it is treated as the electrode resistance, which is fine, but this does not make it Ra.
Ra is a defined quantity, the method you describe results in an approximation, not a measured value, of Ra.

You might as well be stating that g is 10 or that c is 300,000,000
Both are approximations and not the actual values.
 
You are contradicting yourself.
You say it is treated as the electrode resistance, which is fine, but this does not make it Ra.
Ra is a defined quantity, the method you describe results in an approximation, not a measured value, of Ra.

You might as well be stating that g is 10 or that c is 300,000,000
Both are approximations and not the actual values.
Whatever you say dave.........
 
Last edited:

Reply to the thread, titled "PME or TT or Both To Caravan Or Outbuilding" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
PME or TT or Both To Caravan Or Outbuilding
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
Andy Barton,
Last reply from
Ian1981,
Replies
20
Views
6,850

Advert

Back
Top