PME or TT ? | Page 2 | on ElectriciansForums

Discuss PME or TT ? in the UK Electrical Forum area at ElectriciansForums.net

S

sprigsteen

Hi Everyone, New to the site, newly qualified Part P installer. I have encountered two properties which appear to be TT systems with ZE readings of 65 and 100 ohms, on live testing ring main ZS results 0.5ohms and 0.56 ohms. There is no PME earthing connections at DNO cutout fuse. Does this mean the DNO have connected neutral and earth at the pole? How do I know if it is PME? Cheers guys.
 
The OP must have lot the use of his legs, as anyone else would have traced the earthing conductor from the MET looking for the rod............
 
Hi Everyone, New to the site, newly qualified Part P installer. I have encountered two properties which appear to be TT systems with ZE readings of 65 and 100 ohms, on live testing ring main ZS results 0.5ohms and 0.56 ohms. There is no PME earthing connections at DNO cutout fuse. Does this mean the DNO have connected neutral and earth at the pole? How do I know if it is PME? Cheers guys.

Hi Sprigsteen. As you state there is no earth terminals at supply cut out then these properties supplies are not TN-CS they are TT and you should record them as such. The low readings you are getting are parallel earth paths through main bonding and other PME supplies in area. As Zs must be taken with main bonds connected just record what it is and carry on.
 
well well well

and here we go again...

OK:

its all about the PFC here....

do a Zpn...then a Zpe...check results on PFC...

if the same then its more than likely to be a TN-C-S

can you tell us why?

answer please:
One test is live to
earth, the other live to neutral. If neutral and earth are connected by DNO results will be the same. Is this common practice for the DNO? On the installations in question they have the old DNO voltage isolator with the yellow button. Would this have any bearing on the results? Thanks again
 
When testing......PFC.....PSCC.....If same reading obtained it's PME
Thank you driverman. Is it common practice for the DNO to do this? I am assuming they are connecting the neutral and earth at the pole. The installation is protected by old DNO voltage trip with yellow button. Could this have any bearing on test results? Thanks again.
 
We tend to come across them ( all be it far less regularly now days ) mainly whilst testing on old dairy farm supply's and alike .
And to be honest I am very wary of them , as I find once operated with the test button they can be an absolute pig to reengage again if at all .
I agree with you Glenn but for what a main switch and enclosure costs , is it worth the saving ?
 
One test is live to
earth, the other live to neutral. If neutral and earth are connected by DNO results will be the same. Is this common practice for the DNO? On the installations in question they have the old DNO voltage isolator with the yellow button. Would this have any bearing on the results? Thanks again
depends on where they are connected.

do you think the starpoint is common for both neutral & earth?

can you think where there may be another reference point....nearer the installation in question perhaps?
 
I often find installations which have been mixed up when E7 has been installed - the original installation has been TT, but the meter fitter has come to fit an e7 meter/clock/whatever onto a separate board and then connected that board direct onto a PME head and ignored the rest. So within the same house you can find TT and TN-C-S systems running from the same supply that don't cross-over anywhere because the e7 circuits have always stayed separate and no-one has needed to check the bonding.

Until, that is, that house is on the Somerset levels and is sat in 5' of water for a few weeks and all the back boxes start talking to each other through soaking wet walls... it's been fun picking my way through some of my most recent inspections and reports!!
 

Reply to PME or TT ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
926

Similar threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
840
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top