Hello Guys

I have a 200a 3-phase supply PME bolted to a large ryefield panel, the ryefiled panel then supplies 14 flats within the same building.

Each flat is supplied a 63a from ryefild via meters in the form of a 16mm 3core SWA cable.

The furthest away is flat 14 at around 25 meters, seeing as we are exporting the PME supply i would need a minimum 0.05 max between the main bonding in the flats and the MET at the origin (Ryefeild) because the CPC in the SWA is a combined CPC and main bond.

how can i calculate the R2 value alone as looking at table 11 OSG its R1+R2.. would i simply divide by two seeing as the line conductor is the same CSA.
 
Hello Guys

I have a 200a 3-phase supply PME bolted to a large ryefield panel, the ryefiled panel then supplies 14 flats within the same building.

Each flat is supplied a 63a from ryefild via meters in the form of a 16mm 3core SWA cable.

The furthest away is flat 14 at around 25 meters, seeing as we are exporting the PME supply i would need a minimum 0.05 max between the main bonding in the flats and the MET at the origin (Ryefeild) because the CPC in the SWA is a combined CPC and main bond.

how can i calculate the R2 value alone as looking at table 11 OSG its R1+R2.. would i simply divide by two seeing as the line conductor is the same CSA.
Do a long lead test an you will have r2
 
Hi - it’s the size of the incoming DNO supply at the last point where it’s still a PEN conductor, if I’ve understood correctly. Hopefully it’s 50mm or less and you’re good with the 16mm (values from Table 54.8 as you say). The 0.05 Ohms thing is an urban myth :) .
 
The BNO should have the spec of the supply so you can determine the size of the N, if not a quick phone call to your DNO would be the way to proceed.
Your DNO will have a policy document for their requirements for protection for multi way distribution units (Ryefields etc), ask for a copy
 
I cant see why any bonding would be required internally to the flats? Any bonding would need to come from the ryfield/MET to water/gas/structural in prefumanly cellar/switchroom. As other have said, what is dno supply/tails?
 
The water and gas inside the flats are 10mm bonded ... the thing that I am quite confused about is the main bonds for the water and gas coming into the building is one huge 50mm cable.
Then inside the flats 10mm water and gas bonds

There are two main bonds?
 
Main bonding should be installed for each installation.
The installation in each flat is a seperate electrical installation and should have its own main bonding.

If they are being classed as a separate installation, then surely you would base the bonding conductor csa on the supply conductors for the individual installation?
 

Reply to PME supply block of flats in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top