Hello Guys

I have a 200a 3-phase supply PME bolted to a large ryefield panel, the ryefiled panel then supplies 14 flats within the same building.

Each flat is supplied a 63a from ryefild via meters in the form of a 16mm 3core SWA cable.

The furthest away is flat 14 at around 25 meters, seeing as we are exporting the PME supply i would need a minimum 0.05 max between the main bonding in the flats and the MET at the origin (Ryefeild) because the CPC in the SWA is a combined CPC and main bond.

how can i calculate the R2 value alone as looking at table 11 OSG its R1+R2.. would i simply divide by two seeing as the line conductor is the same CSA.
 
Thanks Dave... so going with that and table 54.8, it states selection in accordance with the PEN conductor. So would I need to size the earthing arrangements for each flat according to the main PEN conductor, the PEN conductor at origin is 70mm which would render the CPC of the SWA too small at only 16mm to each flat
 
If they are being classed as a separate installation, then surely you would base the bonding conductor csa on the supply conductors for the individual installation?

No, the size of the bonding is based on the size of the DNO's combined neutral and earth conductor. Neutral current diverted via the bonding under fault conditions will depend on this, not on the size of the supply to each flat.

Ultimately for a job like this the DNO should be consulted.
 
No, the size of the bonding is based on the size of the DNO's combined neutral and earth conductor. Neutral current diverted via the bonding under fault conditions will depend on this, not on the size of the supply to each flat.

Ultimately for a job like this the DNO should be consulted.
Yea that’s how I read it,if you export Pme,then you need to ensure its requirements.
 
No, the size of the bonding is based on the size of the DNO's combined neutral and earth conductor. Neutral current diverted via the bonding under fault conditions will depend on this, not on the size of the supply to each flat.

Ultimately for a job like this the DNO should be consulted.

Agreed, but surely this is why the 50mm bond to structural steel from the ryefield is in place. Also, any of the diverted neutral current from the PEN conductor in fault would also be shared across a number of bonds due to the duplication across units?

In any event I suspect it's all completely hypothetical, if it's a new build with individual gas and water metering, there are unlikely to be any extraneous parts, and if it's an older block with common risers in Iron, then the 'main' main bonds from the ryefield would take care of any stray currents.

In reality, has anyone ever worked on a flat with a 50mm bond anchored to the stopcock?
 
You are not exporting pme at all, the zone is extended not exported which is neither here nore there if it’s all part of the same building complex.
The 0.05 max resistance from the Met to the protective bonding conductors is totally inaccurate and unfortunately is banded about within the industry as a requirement when in fact it’s not.
The 0.05 figure was an indication of measuring between pipe work to determine if the pipes were relatively connected together by a low resistance if the bonding/earthing clamps could not be seen and were ‘built in’.
It’s all covered in GN3 which points out they the 0.05 figure is not between the MET and the bonding conductors.
 
Last edited:
Main bonding should be installed for each installation.
The installation in each flat is a seperate electrical installation and should have its own main bonding.

I disagree and you are contradicting yourself in both posts.. you could segregate one flat to a eicr or eic if works were on going but the OP asks about the ryefield & flats.

No, the size of the bonding is based on the size of the DNO's combined neutral and earth conductor. Neutral current diverted via the bonding under fault conditions will depend on this, not on the size of the supply to each flat.

Ultimately for a job like this the DNO should be consulted.

As there is one DNO supply to the OP property then bonding would need only be carried out from ryefield, in this case 16mm.

Dont know what @cliffed is on about exporting pme :/!!!
 
yes this is true, i spoke with the NICEIC and they say use tabe 54.8 for the ryefield or consult DNO, then each flat cant have any less than 10mm secondary main bonds

You need to install in accordance with BS7671 AND read your DNO policy document such as I linked to in post 18 and comply with this.
This covers bonding requirements towards the end.

Locally my DNO supplies and installs the Ryefield boards because they have had so many instances of refusal to connect to customer installed installations because of non-conformity with their requirements. The NIC are not supplying the electricity, you need to conform with your suppliers requirements
 

Reply to PME supply block of flats in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top