KEVINDOE

Hi all,

Was hoping for a bit of advice on this,
Existing pme supply to domestic house, a supply needed to a shed, an avery,anothershed then a metal framed shed , all these out buildings are strung down a long garden over 40 meters.
My thoughts were to export pme to a submain, lets say Db1, then switch to TT, feed 1st shed and avery{ just a couple sockets in each}, then, take another ciruit from Db1 to another sub, Db2 and TT with additional rod, to feed metal shed and greenhouse, cstomer has requested that all outside circuits can be isolated from inside the house, so i was thinking of r.c.b.o from ccu ?,, are there any issues regarding r.c.b.o and different earthing systems?, radials to Db1+2 will be 6mm swa burried in ground and surfaceing to subs....
would like some advice please ....as this is my first real post, and i am a new member, could anyone just put a reply in so i know its getting seen ? thanks in advance..
 
Last edited by a moderator:
I wouldn't put an RCBO in the main CU in the house. If you're laying SWA then there's no need to use RCD protection for the cable run. You'll already have a 30mA RCD in DB1 for the TT supply, so you'd have to find a time delayed RCBO anyway to provide discrimination.
 
Ok, see where your coming from,, my prob is that the customer wants to be able to isolate all outbuildings from inside the house, so i didnt intend using r.c.d in Db1 or 2, just the r.c.b.o to protect the lot ?

does that make sence ?
 
You could just locate an isolator in a convenient place for the client in the house and keep the rcd for the TT. As there are extraneous conductors in the out buildings i would not export the earth. There are 2 pole lockable ones or i would guess you could use something as simple as a cooker isolator.
 
You could just locate an isolator in a convenient place for the client in the house and keep the rcd for the TT. As there are extraneous conductors in the out buildings i would not export the earth. There are 2 pole lockable ones or i would guess you could use something as simple as a cooker isolator.

Spot on. I would treat DB1 onwards as a separate installation, and keep your RCD there. Have a switchfuse or isolator/MCB combo at the house to supply the submain.
 

Reply to pme to tt in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
931
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top