Hi can someone explain PME for me please, is every house suppose to have it, I worked on building sites and just recently started doing domestic, Iv done few jobs but was told some earthing needs upgrading so obv assumed 10mm for gas and water but was told to look for a pme block????
 
Protective Multiple earthing it is in section 2 of the BS 7671-2008.

After you read that you will see it is a TNC-S system and again you can see section 2 for an explanation which will point you to a further figure 2.4 which is also in section 2 of the BS 7671-2008.

How it is done in the industry is that the DNO bring into their head a Line and Neutral for let's say a single phase supply. Within their cut out they will link the Neutral to an Earth bar and so you have the combined Neutral and Earth at the origin of the installation.

In order to make the system safe at various intervals along that Neutral it will be staked into the ground with Earth spikes all the way back to the Transformer, where it originates.
 
Last edited:
Just out of interest cj, is there an outbuilding with a sub board here? if so then theres issues with "exported earths" and pme......

I'm definitely going to need my pills for this one .............................in the words of Julius Ceasar I'm came I'm saw and I'm buggering off now
 
Just out of interest cj, is there an outbuilding with a sub board here? if so then theres issues with "exported earths" and pme......


Not bad....4 posts until it was mentioned!!!!

Sorry mate no offence intended or anything, it's just we've had some epic threads on PME & exportation/extending etc, and I can see the ususal suspects coming over the hill now.......I'm off!!!!

:tank:
 
Hi can someone explain PME for me please, is every house suppose to have it, I worked on building sites and just recently started doing domestic, Iv done few jobs but was told some earthing needs upgrading so obv assumed 10mm for gas and water but was told to look for a pme block????

This is what the fault loop path looks like, hope it helps a bit.
 
Thanks lenny for the understanding but i just couldn`t help my mischevious self....TEE HEE! On a serious note though i hope it doesn`t ruin what would have been an insiteful thread.....

Have a read of this post: http://www.electriciansforums.net/e...159-good-guide-exported-pme-outbuildings.html

The problem is that the 'you can't export an earth from a PME supply' is in all but some rare cases, just not true.

There may be economic reasons because of bonding conductor sizes and costs.
 
YOU ARE NOT ALLOWED TO EXPORT AN EARTH ON A PME!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!

oh yes you can
oh no you cant
ooh yes you can
ooh no you cant
oooh yes you can
oooh no you cant
ooooh yes you can
ooooh no you cant
oooooh yes you can
oooooh no you cant
ooooooh yes you can
ooooooh no you cant
 
Just looked at it IQ and what they are refering to is earth bonding of any gas and water pipes which would have to go back to the met at the main dis board (not to the met at the sub board). And also the seperation between exposed conductive parts being protected by 2 different types of earthing arrangements ( to prevent different potentials).

All you are doing is ''Expanding'' the equipotential zone, ...Your NOT exporting it, when you connect a bonding cable to any extranious pipework at the new location.
 
All you are doing is ''Expanding'' the equipotential zone, ...Your NOT exporting it, when you connect a bonding cable to any extranious pipework at the new location.

That sums it up perfectly, if you have a decent understanding of protective bonding with a view to bringing an area into the equipotential zone then any PME mysteries are gone!

Obviously with the exception of the specific instances ie. caravan supplies where this scenario is forbidden.
 
So in effect 54 you can export a pme earth to lighting and points etc in an outbuilding but when it comes to pipework etc this has to be on an extention of the equipotential zone so would still require a separate earth pulling in going back to the main met....

It can be within a multicore cable or an armoured cable SWA earth as long as the CSA meets the requirements.
 
So what you are saying IQ is as long as your R2 is good (0.05 ohms) using the armoured then its good.........

No, it's down to size (the continuity would still need to be proven but not recorded).

The 0.05 Ohms is more to do with resistance between extraneous-conductive parts to establish the effectiveness of supplementary bonding.

Check out 544.1.1 and Table 54.8
 
No, ....If you were to use the cables SWA as your bonding conductor, it would need to have the equivalent CSA of 10mm Copper, not 10mm CSA of steel!!!


So really, you have a choice of installing a correctly sized SWA cable for your supply needs and a separate 10mm single bonding conductor, ...OR 10mm or greater SWA cable with a separate core to be used as your bonding conductor, and using the SWA as your CPC....

Look up the K ratings of Copper and Steel in the BRB, or other publications and you'll see what i mean...
 

Reply to Pme in the Australia area at ElectriciansForums.net

Similar threads

  • Question
In the mind of someone lying there wide awake at 3AM, just about anything.
    • Like
2
Replies
25
Views
2K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top