Pme

S

sedgy34

got a tns at 1 ohms dno will give us a pme for £180 or they say shove a rod in the ground ummm im thinking is there much price in it but the pme is guaranteed the ze on the rod could be varaible with the dryness of the soil what are your thoughts guys.
 
I know it would be froned upon, but i would use a roll spring, and improve that existing earth. Before doing thatbthough, have you tried taking a Ze, with the earth probe on the exposed metal sheath of the supply cable?
 
Ask them if the bonding is only 6mm and they change the earthing to PME are they going to stand the cost of upgrading the bonding to 10mm to comply with regs. Charging to sort out their problems, genius.
 
Ask them if the bonding is only 6mm and they change the earthing to PME are they going to stand the cost of upgrading the bonding to 10mm to comply with regs. Charging to sort out their problems, genius.

we have 10mm bonds in place as we have rewired the property
 
i just had to have a pme upgrade for a customer, £136 from western power "south west"
ze was .20 at the sheath but wire broke off many years ago,
bet the guy that came could have slapped a 3m clamp and braid on the sheath, but no they have to pme upgrade.

asked this question before, anyone know where i can buy 3m constant pressure springs and 16 mm earth braid kits from please????
 
got a tns at 1 ohms no will give us a pme for £180 or they say shove a rod in the ground ummm im thinking is there much price in it but the pen is guaranteed the zeon the rod could be variable with the dryness of the soil what are your thoughts guys.


They try it on every time these DNO's!! They have a DUTY to maintain any earth connection they have previously provided... Don't take any crap, insist they stand-up to their responsibilities...
 
Last edited by a moderator:
They try it on every time these DNO's!! They have a DUTY to maintain any earth connection they have previously provided... Don't take any crap, insist they stand-up to their responsibilities...

is there anything to back that up so i can go then guns blazing:gunsmilie:i know they will try and fob me off
 
is there anything to back that up so i can go then guns blazing:gunsmilie:i know they will try and fob me off
right, then dont be fobbed off sedg......as eng has quite rightly pointed out already....if the install was already using the distributers facility as a means of earthing when the fault/high impedence was discovered and reported then they have a duty to maintain it....end of......dont let em slip out of this like a fillet of wet fish....insist they sort it.....or threaten em with a watchdog...or whatever governs em....
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
sedgy34,
Last reply from
Silly Sausage,
Replies
16
Views
3,154

Advert

TrueNAS JBOD Storage Server

Back
Top