The guy that works for me doing some of the electrical bits connected one of the new IMO isolators the other day. When I checked on commisioning the polarity was wrong. rather than connecting in a stright line through the isolator the connection goes accross, so the top left input is continuous with the bottom right output, top right with bottom left.
 
I HATE IMO! Used them once and never again. To small and illogical layout. I like a bit of space around the isolator to allow for cable curving not cable cramming.
 
Guys,

On an AC isolator, it is physically possible to have the input and output of each pole in the same plane - the contacts separate in a 180degree plane away from each other. With a true DC disconnector, especially the IMO products, the contacts are intentionally designed to rotate/slide apart (or together) to minimise arc formation and to allow self-cleaning. These functions of the design are intentional as part of the unit's ability to manage load breaking DC current and to maximise the life-expectancy of the product.

If you look closely at the contact block/base, you will see that each pole (1-2, 3-4, 5-6 & 7-8) is actually stepped from each other - to facilitate this rotational knife-edge contact design.

Anyone using a contact block that has straight pass-through of contacts is more than likely looking at an AC contact block, not DC....

As for space inside the enclosures, this is a common observation, especially when running 2 strings through a 4-pole unit, and especially when running 6mm2 wire. However, IMO have listened to the marketplace and all new products being manufactured and supplied since the last couple of weeks now have the new, longer enclosures giving more working room inside and around the terminals.

Hope this helps,

Andy
 

Reply to polarity warning on IMO isolators in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
603
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
304
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
955

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top