Can you really rely on testers to confirm polarity doing a Zs? im not convinced

Is doing an R1+R2 the only way to guarente?
 
Depends on the circuit you are testing.
For instance the only way to prove the polarity of a radial socket circuit is to visually check it.
For a ring main you have to do a full ring test.
 
Can you really rely on testers to confirm polarity doing a Zs
Can I rely on testers...? Surely what you want to ask is: can YOU rely on testers...?
What I can do with a tester might be different to what you can do with a tester.
I know what I would like to do with a tester, sometimes :)
Have you ever tried to do a Zs test on a reverse-polarity circuit?
 
Nope...

But polarity should be proved before carrying out any live test including ZS :)

spoilsport..... switch on and confirm polarity with finger. the brown should be the one that tingles. also doubles as RCD trip test. ( don't try this at home, children).
 
After having read most of your posts REGS I really couldn't work out how and why someone with your skills and abilities could make these posts.

According to your good self you have a high intellect and the ability to pass the 2391 with great ease.
You have gone through all the training and selection processes required to become a serving policeman, this in itself implies all sorts of skills and personality traits.


Soooo I decided to do some research and came up with this..


[ElectriciansForums.net] Polarity
 
It was a genuine question that can testers be relied on that if you wanted to do a quick check on socket(s) do you think they give accurate feedback to the end user? whats wrong in this question? there are so many different one's on the market. You even get those cheap 1's for 20 quid that give the 3 light indication. If its crap and unreliable i want to throw it before an accident. You all keep banging on about safety, this relates completely to safety and still all silly childish remarks.

In answer to above post of course i've tried reverse polarity with my megger which it will detect no problem. The whole reason for the post was if you switch the earth and neutral around they don't pick it up.
 

Reply to Polarity in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
701
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
301

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top