As above says, when testing ir on three circuits I put each circuits neutral into the line into the mcb and tested from mcb terminal to earth, each result below 1M, I then tried connecting the line and neutral in a terminal block , and the results shot up?????

This consumer unit is in a cold outdoor cupboard as per pics I will post, it did the same on all 3 mcbs on the right hand side, all mcbs where switched down in case anyone asks.

My thoughts where dampness or something wrong with mcbs?
 
I'm just wondering, depending on how you carried out your test, if using 500v and conditions inside MCB/RCD were damp, you could get reading through devices, even if they were turned off?

I tested all at 250v getting about 1M with n-l connected in mcb switched off and when tested at 500v I got about 0.05 yet when connected in a terminal block out of mcb I was getting 30M plus
 
Teste across one of the mcbs at 250v and then 500v and at 250v it came up at 81M and at 500v it came up at about 62M

Thoughts?
Should this be above what the tester can read?
If so would this be the damp getting in and would you cod this c2 or c3 in an EICR?
 
Teste across one of the mcbs at 250v and then 500v and at 250v it came up at 81M and at 500v it came up at about 62M

Thoughts?
Should this be above what the tester can read?
If so would this be the damp getting in and would you cod this c2 or c3 in an EICR?

why would you code anything? The readings in your example above are way above what is ok
 
why would you code anything? The readings in your example above are way above what is ok

I would say they are not ok for a test applied between incoming and outgoing terminals of an MCB in the open position, the reading should be far higher and it is a sign that the MCB has become damaged, most likely through moisture ingress in this situation.
 
I tested all at 250v getting about 1M with n-l connected in mcb switched off and when tested at 500v I got about 0.05 yet when connected in a terminal block out of mcb I was getting 30M plus
As others have said, perhaps the mcb's have become faulty. Don't understand why your using the mcb's as a connector to do your IR tests, or are you just curious now?
 
Try continuing the IR test across the MCB and see if the reading slowly rises, if so then this is a possible sign of dampness that is being cleared by the testing. If the reading is stable then this would be more likely an MCB fault, however that would be odd for all three if it is not moisture.
I assume there are no signs of overheating of the local busbar?

Though of course if there is a connection through the MCB then it may be picking up the RCD, that could give a low reading.
 
If you are concerned,remove the MCB altogether,and test independently. Then test a known good one,or a new item,and compare...

It has been mentioned that the values are acceptable,but being mindful of the short distance you you are testing across,the likely cause of these readings,and the certainty of a customers digit being applied to it...

If it is on your mind,and the length of this thread ,suggests that,i recommend attending to both the cause,and effect of the issue....

Which may be as simple as a ÂŁ3 MCB,and an umbrella....
 

Reply to Poor ir on when connected to mcb in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
792
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top