Hi guys looking for some guidance ,i am assisting with the renovation of an old building that contains a commercial kitchen and restaurant the building is in no way wired to commercial spec but has been passed electrically in the past. Very little information was present at all 4 fuse boards and as the building is on a TT system is fitted with a main 3 phase 30ma rcd which i had to disconnect to find all the faults (it has now been replaced with a 100ma one to help with nuisance tripping ) The main problem i had was that according to information at hand gp3 and 4 were fed from the same 32a mcb both boards were disconnected and i did an insulation test to find a dead short . Further investigation and a lot of floor board lifting and i found the swa feeding gp4 had been cut and joined with a hightough cable going to gp3 using a resin joint that i have used previously on underground cables for street lighting and which i have known to go faulty so i have run new cables one from gp1 to gp4 in 10mm t&e which is 22m long and a 6mm t&e which is 20meters long . We have bought in the local guy who has inspected the building before and he wanted to know why this had been done so i explained and showed him the joint he did seem a little sheepish after that and and some of the c2s on his report i am convinced are copied and pasted from the last one! but he has stated that gp4 has a poor cpc r1+r2 earth reading but not said what it is. Could someome please tell me what i should have its a long time since i did any testing and want it sorted sorry to be so long winded but wanted to give you the full picture