Thats what I thought, but they are saying it will stop the system working. The office are also trying to put me off by putting the responsibility on me, by saying they will do it but the consequences are down to me.
Bonding and earthing are two separate things, something that appears to cause confusion,
Bonding is when you join two conductive materials together, like the copper pipes under your sink.
Earthing is when you take a wire back to an earthing point, and with most (not all) PV systems, this would be to a metal rod in the ground.
So it sounds like your system needs bonding and earthing, not really too difficult or expensive if they are already up there.
I hope this helps.
Both bonding and earthing should eventually be connected to the main earthing terminal - supplementary bonding is just an extension of this.
Earthing works by keeping disconnection times as short as possible, bonding is concerned with the magnitude of any shock - if the all metalwork is at an equipotential then there should be no voltages present between them under fault conditions.
As PV panels and the frames have no disconnection devices in the system then earthing is irrelevant.
No, it needs to be 10mm at least.
They are 1 course of tiles from the eves.
the orientation of that array is east, the flue doesnt seem to affect yield.
Just been up on the flat roof and noticed that the clamps on the right side are only attached to the rail by about 2-3 mm :dizzy2:
Have just asked them to sort it out.
Shame they couldn't be bothered to notch the back of the tiles out so they sit flush. Wind and wind driven rain will find its way up there for sure.