Hello :)
Just been doing some investigations into running power from the CU in the house out to my shed.
I lifted the floorboards on the upstairs landing and found that power cables have been laid right next to the central heating water pipes.
This can’t be safe, surely?
 
Hello :)
Just been doing some investigations into running power from the CU in the house out to my shed.
I lifted the floorboards on the upstairs landing and found that power cables have been laid right next to the central heating water pipes.
This can’t be safe, surely?

A pic would be great. The cables should not be in close proximity to any hot water pipes. Unless the cable has been sized for such an environment.
 
[ElectriciansForums.net] Power cables and hot water pipes.
 
You see that sort of stuff all over the place. Not best practice, but not life threatening. It has been working like that for a l-o-n-g time, looking at the cables.

I would be more concerned about the structural soundness of the joists, especially if it’s neighbours are chopped in a similar way!
 
Yes, not correctly done but certainly not rare. Since you've got it apart perhaps have a close look for any heat damage, hopefully it will be ok.
 
Not unusual ............ this is obviously an older installation.

Certainly wouldn't do it that we these days ....................
 
I've seen plenty cables installed as above, damaged through heat to the point of sheath and insulation failure, and the inevitable fault of negligible impedance type bangs.
 
is that a joist or a noggin looks to be running in the same direction as the floor boards
 
Bit rough but if you lag the pipes it should be fine.
Maybe up to the joists it's a shame that one of the cables is wrapped over the pipe as you could have bunched cables central between the pipes and inserted an insulating shielding each side and a safe plate over + marking on the floor above if not rewiring.
 
You see that sort of stuff all over the place. Not best practice, but not life threatening. It has been working like that for a l-o-n-g time, looking at the cables.

I would be more concerned about the structural soundness of the joists, especially if it’s neighbours are chopped in a similar way!
It always makes me laugh when I see the great big chunks taken out by the plumber for the water pipes yet we have strict criteria on the size and position of holes we make for the cables. :)
 

Reply to Power cables and hot water pipes. in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

J
  • Article
Have my water pipes been plumbed the wrong way? Good morning, I recently had an extension, new bathroom and new en-suite fitted. Prior to the...
Replies
0
Views
289
jennys07
J
C
  • Article
Noisy main cold water pipe, my plumber hasn't heard this before. Hi Folks, Would like to cast the net far and wide to try and get some resolution...
Replies
0
Views
201
ComfortablyNumb
C

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top