S
Smudge
I am after a little help if anyone can, on a problem i've been given at the factory i work in...
We have a limit on our supply capacity we are allowed to use (950kVA) before we get hit with extra charges. Using our own energy monitors, our usage (max) is approximately 880kVA over the last couple of days, and that seems to be the normal sort of load over recent weeks too.
Our problem now is that we want to install a new bit of plant that has a potential demand of around 150kW, pushing us way over our capacity allowance. Upon some quick readings we have taken from the energy meters, they are saying we are achieving a p.f. of around 0.904. After some research, i have come across a general view that the p.f. should be greater than 0.95. We have capacitors on our incoming already, however, these would have been sized at a time before some rapid growth of our plant, and haven't been given any attention since they were put in >10years ago.
How can i check if they are the correct size? Are they easily maintained? And how can i explain to the boss's above that improving p.f. can help achieve greater capacity and lower costs?!?
thanks for reading
We have a limit on our supply capacity we are allowed to use (950kVA) before we get hit with extra charges. Using our own energy monitors, our usage (max) is approximately 880kVA over the last couple of days, and that seems to be the normal sort of load over recent weeks too.
Our problem now is that we want to install a new bit of plant that has a potential demand of around 150kW, pushing us way over our capacity allowance. Upon some quick readings we have taken from the energy meters, they are saying we are achieving a p.f. of around 0.904. After some research, i have come across a general view that the p.f. should be greater than 0.95. We have capacitors on our incoming already, however, these would have been sized at a time before some rapid growth of our plant, and haven't been given any attention since they were put in >10years ago.
How can i check if they are the correct size? Are they easily maintained? And how can i explain to the boss's above that improving p.f. can help achieve greater capacity and lower costs?!?
thanks for reading