revising for my 301 on Thursday and Ive come stuck on a question, any ideas?



A 30KW 3 phase delta connected motor has a power factor of 0.86 lagging. Calculate the line current.

answer is 50.35a but i dont know how to get there





thanks in advance :)
 
Last edited by a moderator:
erm another quick problem.......


A medium sized factory has a three phase load of 50kVA and 30kVAr. Calculate the power factor?

a. 0.8



again im struggling with the formula, i must be arranging it in the wrong order, sorry to be a pain but anybody help us out?
 
Upvote 0
post the formulae, what is 30kvAr, should that read 30kvA, is 50kvA apparent power and 30kvA true power?
 
Last edited by a moderator:
Upvote 0
well it will be this wont it?

The power factor for a three-phase electric motor can be expressed as:
PF = P / [(3)1/2 U I] (2)
where
PF = power factor
P = power applied (W, watts)
U = voltage (V)
I = current (A, amps)
 
Upvote 0
sorry i must be using the wrong forumula then, this is exactly how the question reads:


A medium sized factory has a three phase load of 50 kVA and 30 kVAr. Calculate the power factor
 
Upvote 0
to me, and im pretty sure im right(99.9%), you have a factory with apparent power 50kvA and true power of 30kvA, power factor=true power/apparent power, 30kvA/50kvA=0.6 which means your answer is wrong. text books with incorrect answers are not uncommon. does this sound plausible?? also i'm not sure what kvAr is?
 
Upvote 0
to me, and im pretty sure im right(99.9%), you have a factory with apparent power 50kvA and true power of 30kvA, power factor=true power/apparent power, 30kvA/50kvA=0.6 which means your answer is wrong. text books with incorrect answers are not uncommon. does this sound plausible?? also i'm not sure what kvAr is?

kvar is Reactive Power so i think the question is right im just not getting it. :confused:

or you could be right and the paper is wrong lol
 
Upvote 0
you are right, i didnt think you would that at level 3, i cant cope with these questions after a few beers so ill get back to you tomorrow nite if thats ok
 
Upvote 0

Reply to Power factor question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
Received guidance from a logical soul on the Kawie Riders forum: Acc Fuse Block Power to BAT LOAD, install new cable from BAT LINE to AUX + (and)...
Replies
1
Views
372
  • Question
It's the policy on this forum not to give step by step advice. If you have an understanding of wiring requirements you will not have any...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top