DT1878
revising for my 301 on Thursday and Ive come stuck on a question, any ideas?
A 30KW 3 phase delta connected motor has a power factor of 0.86 lagging. Calculate the line current.
answer is 50.35a but i dont know how to get there
thanks in advance :)
erm another quick problem.......
A medium sized factory has a three phase load of 50kVA and 30kVAr. Calculate the power factor?
a. 0.8
again im struggling with the formula, i must be arranging it in the wrong order, sorry to be a pain but anybody help us out?
pythagorus gets you true power at 40kw.
then 40/50 = 0.8
edit; just to put a bit more meat on the bones of it - its your power triangle that you need to know , with kVA on the hypotenuse , kW on the adjacent and kVAr on the opposite.
(notice it is another 3, 4, 5 triangle)
Upvote 0
had a look through my HNC notes and icant give you an answer from those two figures, i would need the phase angle between the supply voltage and the supply current or use as pushrod says pythgorus with impedance triangle of the reactive component with impedance (Z) on the hypotenuse,resistance (R) on the adjacent and reactance(X) on the opposite,
that make any sense???:)
Upvote 0
then 40/50 = 0.8
actually that makes far more sense, im over complicating it, but the cosine of the phase angle equals the power factor
Upvote 0
This is what you need to know.( It is very similar to the impedance triangle)
VA² = W² + VAr²
so in your example W² = VA² - VAr²
W = sq rt ( VA² - VAr² )
W = sq rt (50² - 30²)
W = 40 k watts
Power factor = real power ÷ apparent power
= 40 ÷ 50
= 0.8
hope that is a bit clearer - if it isn't at least try and remember that since the hypotenuse part of the triangle is the longest that means that the VA figure will be bigger than the W.
So if the question says the apparent power is 15 VA what is the true power in watts you at least know you are looking for a smaller answer:)
Upvote 0
VA² = W² + VAr²
W = 40 k watts
= 40 ÷ 50
= 0.8
Glad to see you're making use of the ² & ÷ symbols, but what about poor old :D
Really good stuff by the way
Upvote 0
i couldn't find it in the full list of html codes , but now i see you actually included that one in your actual post - DOH!:o
Yer just had a look at list. Not as big as I thought it was. I must have got them from a different website. If I find it again I'll post it up.
Upvote 0
VA² = W² + VAr²
W = 40 k watts
= 40 ÷ 50
= 0.8
Would I be right in saying that
VA = √(W² + VAr²)
W = √(VA² - VAr²)
VAr = √(VA² - W²)
Seems to work with the 30, 40, 50 from this thread.
Upvote 0
Here's another good way of remembering it (for me anyway :))
S = Apparent Power (VA), P = True Power (W), Q = Reactive Power (VAr)
S = √(P² + Q²)
P = √(S² - Q²)
Q = √(S² - P²)
PF (Power Factor) = P ÷ S
Upvote 0