its the RCD protecting the circuit had this on sunny boy inverters before you need 100ma RCD
it's the inverter cutting out though, not the RCD.

the inverters have an inbuilt all pole RCMU system, I think it's set to 50mA leakage current, but I can't entirely remember where I found that info.
 
I've been doing some digging and i think it might be set to an insulation resistance value of 1MOhm on TLs, HFs is much lower at 0.2MOhms and will only generate a warning rather than a fault because of the separation.

The Mini Central's were changed via firmware a couple of years ago because of this problem but everyone i've spoken to at SMA say it isn't the issue.

From SMA

'The inverter type Sunny Mini Central SMC 9000TL/10000TL/11000TL is equipped with a measurement technology that goes well beyond the test conditions demanded in the standard and is capable of identifying insulation errors that can be difficult to detect. In order to meet the limiting value of 700 k Ω required by DIN VDE 0126-1-1, the devices were delivered with a limiting value of 900 k Ω .'

and

'As of December 1, 2010, SMA Solar Technology AG delivers the Sunny Mini Central 9000TL/10000TL/11000TL with a firmware where the limiting values for the insulation resistance were adapted to the new
general conditions. SMA Solar Technology offers this firmware as a free update on request for all previously
delivered inverters. The new thresholds ensure that the PV plants run safely and only actual insulation failures
(module break, marten bites) are reported as a disturbance.'
 
We had a trio 20kw fail last summer. Bad batch of components apparently. None since but we haven't done a huge amount of them.

Also had a 3.6tl fail, 1st failure of many installed.
 

Reply to Power One Problems in the Green Lounge (Access Only) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
749
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
376
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top