nsa100

I have recently had Aurora Power-One PVI-3600 Inverter installed. I saw that thee Wireless module had 2 flashing LED when installed.

They also supplied a PVI-Desktop Monitor, but when we try scanning for the inverter it does not find it, and after 2 mins of scanning it says scan error.

It will not connect even with the monitor in close proximity to the inverter.

We have tried powering down both the inverter and monitor.

We tried pressing the small reset button on the wireless monitor

Any ideas.
 
I suspect they didn't install the wireless piggy back unit in the inverter, which doesn't come as standard with aurora.
 
Is it indoor or outdoor?

If its indoor it doesnt require an extension lead and the antenna screws directly into the antenna socket underneath.
This plugs into port 2 and should have a flashing green light on the circuit board inside. If you have 2 flashing orange lights it sounds like the card was installed when the inverter was already on and it may have blown the inputs on the module but more worringly it may have permanenetly damaged the inverter inputs.

You may get away with replacing the module but you may have to replace the inverter if you wish to continue using the remote monitoring.

I spoke to Power One last week about exactly the same problem and what you have read is what i was told.

Sorry if that pis**s on your parade bud.
 
Last edited by a moderator:

Reply to Power-One PVI-Wireless Module in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

  • Sticky
Hi Richard, thanks for your comment. The relay is rated 12A peak. It's also worth noting that a relay contact will perform differently depending...
    • Like
    • Winner
Replies
4
Views
2K
  • Question
Thanks Chaps..... do appreciate all your advice as usual 🤩🤩 Think we've finally got there 'after visit 5'! 🤞 Sticking with the V-Pro, chatted...
Replies
9
Views
1K
it's common for a PIR to activate on restoration of power.it should however swich the light off after whatever time has bee set.
Replies
2
Views
3K
Just doing some thread admin :)
Replies
1
Views
808
There are a few choices, one way or another it will connect at 240V AC into your house wiring system. It really depends where the panel is wrt...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks