Hi All,
Just looking for some reassurance on a job I've looked at today. My status is that I am trying to stay within the realms of 'Minor Works' until I get a bit of experience under my belt. Conscientious decision - but everywhere I go it seems that notifiable work is needed as well. Anyway......
So - a customer has asked me to supply power to an outside office that's about to be built (when it stops raining), and has asked if I can take the supply from a nearby external supply he has spotted (actually supplies a pond). I've done my homework, read around the subject.
TNCS
Pond Supply = 2.5mm but spurred from B32 Ring Final.
Tested (live) Zs near the pond at 1.28 ohms so already a bit naughty.
Ring Final IS RCD protected.
The outbuilding has no extraneous conductive parts.
Not sure on the demand for the office but its pretty small, it has its own 'garage unit' (apparently) so suspect a B16 for sockets and B6 for lights.
New building is a gnats whisker from the man house and ring final.
It needs a new circuit - doesn't it?
I'm clutching at straws because the consumer unit is a long way from the new building, and running a new circuit will be a fair amount of work for a few sockets and a light.
I'm toying with taking another fused spur from the same ring (if Zs is low enough), through the walls and into the new building.
What then though - I understand you need a double pole isolator in the new office - but do I ignore the 'garage' consumer unit or use it? Maybe run a 4mm from the house ring final spur to the garage unit? Not ideal, but if Zs (or Zdb) in limits at the garage unit.....
I'll be interested to hear your thoughts and opinions.....
If you are going down this route then just make sure you state the max 13A supply in your quote and explain this to the customer.
Got to C.Y.A. if the customer decides to put 3 heater into the place then whinges..
Are the cable calcs ok for Zs and other rubbish?
It's the cable calculations I'm looking at now. It's a bit close to the mark with the B32. It's probably best if I do dead tests instead of live Zs Tests through the main board RCD...
I like the idea of stating the max 13 amp. on the quote though. Makes sense.
If you are running the supply from a 13A FCU, then what is the point of this second CU?
You won’t get any discrimination, and the source ring final is already RCD protected, so you don’t need another one!
This needs a separate circuit. Sorry if this is outside your experience/ability.
Park it and walk away.
Yes. I’d say so. Biggest demand likely to be the heater.
Can’t see the 13 amp fuse blowing in the spur...
I'd say there is every chance of the fuse blowing. Heater/PC/Printer/TV/Fridge/Vacuum Cleaner etc etc.
Also I find modern Fused Spurs (of pretty much any brand) are pretty garbage if anything like 2-3kW is the load for long periods of time
Yeah. I might give the customer a choice.
60 metres of SWA and labour (and an RCBO)
Or 4metres of Twin and Earth.
I wonder what they'll go for?
Hold on ................ 60m of SWA or 4m of T&E ................ can you explain
And I would NOT be recommending anybody that they try and run a garden office off a 13A spur......................
Thanks. I know I wouldn't get discrimination.....
I was thinking the Zs might creep up too high for ADS if I didn't use the garage unit....but then again it's not really a sub main, it's a spur from a ring final. It all sounds like a bit of a hash up..
Your honest reply is appreciated!
New circuit from the consumer unit on one side of the property to the other- probably around the outside (there is no easy route). Or 4m from the ring final through a wall...
I might have exaggerated with the 60m.....not really looked at the new circuit options properly yet. Cc
Let me see if I can get some more info on the likely demand.
But TBH - from what I am hearing here it just makes me want to let go of those straws!
I did see an abandoned 6mm T and E in the consumer unit - unwanted supply for an electric shower maybe?
I wonder where that goes.....
If they can afford a new garden office then they should really put in a proper dedicated supply .........................
How many times do people buy something, like a garage office or kitchen and are not thinking about the supply? It's what people do.. they don't like spending on electrics, things they can't see.
I'd still give the customer both options. See which one they want. 13A may be enough.
Talk to them and tell them what they could possibly get for their 13A.. 1 PC, Printer, 2kW Heater, TV........etc
Hi All,
TNCS
No point in spurring the outbuilding with a 4mm2 cable from a ring final wired in 2,5mm2, spurring the office, the office will be limited by the fused spur you have spurred from, in this case 13Amps, "what does that tell you?
Your best be would be to do the job properly and run a new supply from the house CU.
had one of these myself to quote for, main CU 45metres from "office" or glorified shed, 10mm to supply a new CU, chances are theres going to be kettle, fridge, lights, pc, printer, t.v, heater etc.
better to have spare than not enough.
Fair enough. It probably is only about 500 MM of cable from FCU in the house to the first socket in the office!
Send him off to a shed and tell him to buy 2 x 10 meter extension leads then ............ probably less than £20 and he can have 26A ....
In my experience, if you’re ever at that point where you’re clutching at straws or you’re leaning towards to wrong side of the fence, it’s best to write the idea off and just put it to the customer and tell them how it is, as much as they don’t like it. :)
Falls under C.Y.A somewhere..
Zs shouldn't be an issue as that part of the circuit will be protected by a BS1362 13A fuse.
Well - I just looked through a lot of old posts with regards to this. I understand the Physics which says this is safe if disconnection times met, but not convinced it's compliant.
It's relevant to me right now, as a separate job on this site was to add additional external lights to an existing outside light - maybe 40m of cable. When I investigated the existing light it also turned out to be on spur from the same ring final as the mentioned before. It would take the Zs way over the max allowed for the OCPD.
Hmmmn. Need to get off the fence with this one. Tricky. Certainly would be useful to extend Spurs beyond their OCPD Max Zs limits - but is it compliant?
Marcus, if it is that close, why not just extend the house ring into the office and provide a 3A FCU in there to provide power for the lights?
No new circuits, no new consumer unit, just a double length of 2.5mm T&E ???
Good option that. Not too difficult either. There are sockets either side of a fireplace in the house and the office will be on the other side of that wall. Heavy duty conduit straight out and through the whole lot. Lovely. Best do my proper dead test and make sure I can get a few more meters of cable into the ring. Lovely!
Depends how big an office it is. If it's 1 computer a desk lamp and a small heater (which is not unthinkable) I wouldn't have a problem with running it through a fused spur. If it's bigger and they're going to be whacking multuple heaters and stuff on then it's a no no.
Looking at a job first hand the straight forward solution suggested in post 26 should have been in your thoughts from the outset,particularly as its just through the wall
Sheffield
United Kingdom
Power to an Outside Office - Spur from Ring Final?
Marcus Vaughan,
Des 56,