I have just had a call from a company who are looking at installing some elctric gates at the bottom of a long drive.
They have asked me to price for 100m armoured cable (its a looooooong drive).

I asked the guy what amps i need to power the gates and he replyed 6a.(prolly less than this but thats what he said)
They want the cable clipped to the fence down the side of the drive.

I was just looking at what the voltage drop may be for this cable so turned to page 338 and 339 of the bgb.

Now i like to use 3 core armoured cable i was wondering which colomn i should use
p339 colomn 2 says 2 core dc, colomn 3 says 2 core single phase ac and colomn 4 says 3 or 4 core 3phase,
no colomn for 3 core single phase.

do i use cololmn 3 or 4?

Thanks in advance guys
 
treat it as 2 core a.c. single phase. the 3rd core is used as cpc, so will not count in the VD equation. top of my head, at 6A yo'll get 12V drop using 2.5mm
 
I would go with 4mm TBH. No doubt they may want automatic lighting connecting etc and as mentioned possibly a socket as it's always handy to have.

How are they controlling the gates?
 
The last set of gates I looked at were controlled by remote fobs and door entry type system wired (camera and all the gubbins) in Cat5, only a 25m run so not sure how Cat5 would hold up over 100m.
 
The last set of gates I looked at were controlled by remote fobs and door entry type system wired (camera and all the gubbins) in Cat5, only a 25m run so not sure how Cat5 would hold up over 100m.[/QUOT


wouldn't like to bury cat5 direct in the ground.LOL>
 

Reply to Power To Electric Gate in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

Similar threads

I've been fitting CAME gate kits. They are very adaptive, have intercoms, keypads, fobs, autodialers entry exit. They also do a lot of wireless...
Replies
1
Views
292
The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Replies
2
Views
273

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top