It's all confusing, time for another southern comfort.

Yeah I think you might have missed my point. No worries, might have a little snifter myself. Cheers!
 
Access to single insulated cables without the use of a tool. Oooh I'm in a mischievous mood today:)
Would someone be so kind as to give me a Reg No. for this?
 
"521.10.1
Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking.
Non-sheathed cables are permitted if the cable trunking system provides at least the degree of protection IPXXD or IP4X, and if the cover can only be removed by means of a tool or a deliberate action."

The last bit about deliberate action is a little vague in its intent...
 
"521.10.1
Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking.
Non-sheathed cables are permitted if the cable trunking system provides at least the degree of protection IPXXD or IP4X, and if the cover can only be removed by means of a tool or a deliberate action."

The last bit about deliberate action is a little vague in its intent...

Good find. Cheers!
 
I hadn't come across IPXXD before. From a quick Google it seems a way of establishing safety by testing - using a probe 1mm dia and 100mm long and checking it cannot come into contact with live parts. As stated, single insulated cable is not regarded as a live part.
It seems a bit extreme to poke a probe into every hole in a completed length of trunking, but doing a sample would be one way of demonstrating the trunking is compliant (that is assuming the trunking has a cover requiring a tool to remove)

I think there's grounds for challenging the C2, unless I've missed something 🤔

From Voltimum (so it must be true 🤪):-

IPXXD:

For this degree of protection, only the third letter ‘D’ is relevant. The letter ‘X’ signifies that the first and second letter protection levels are not specified. BS EN 60529:1992 + A2:2013 states the requirement for ‘D’ as the degree of protection required for protection of persons against access to ‘hazardous parts’. An access probe having a maximum diameter of 1mm and maximum length of 100 mm, when inserted into any gap or joint within an enclosure with an applied force of 1 Newton, must not make contact with ‘hazardous parts’.
 

Reply to Pre-drilled holes in trunking EICR Code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top