B

beefheart

hi

Ive got a customer that has a meter position about 400 metres from there house intake, they want to install an groundmount system that is then 218 meters from house, i can account from for the pv side but what does everyone think about the supply side, admittedly this has only come to light via email so i will need a more in depth site visit to check the cable and exact length, anything else i should consider, what should I look out for ?
 
Try the SunnyDesign software. voltage drop will be your biggest problem (oh! and put the gen meter near the inverter :) )
 
With our recent experience You HAVE to make some serious cable calculations and voltage readings before making a decision and the cable calculations HAVE to be made right back to the origin of the supply. The generation meter next to the inverter is good idea and good practice however VD and high voltage will mean the inverter WILL drop out at peak generation times. Don't rely on a sub main being suitable not only for load but it would not of been designed factoring in the <1% VD (if designed at all!) See my post on Diehl AKO Platinum 3800S Dropping out. 250mts @ 50mm. Not enough.
 

Reply to private supply cable 400 metres from meter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
948
Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top