The functional earth leakage exist usually on computers and such that have a deliberate functional earth facility, for the sound operation of those appliances
Household junk is usually leakage free, unless there is a deterioration in the appliance itself
Circuits with rcd protection should be split up to an extent that a leakage on that circuit does not take out other circuits
Its a consequence of the rcd anything regulations that we may have these sort of problems
A full rcbo board that takes out only that circuit was what was envisaged by the 17th regs,but economic reality played a part and split rcd boards were accepted as the norm
These however have a very fatal weakness, as you may have found.
Multiple appliances with a little leakage on each can accumalate to trip the rcd where no real problem is evident
If the problem has been diagnosed and found to be the freezer,then why not first measure the amount of leakage and act on whats found
I dont think looking for answers with protective conductor currents is the best approach, nor the modification of the installation to suit an appliance that is not operating now the same as when it was manufactured