M

martin1966

Can anyone help me with my di log 9083P tester i need to know if i am using the tester correctly I am not sure if i am using the ZE/ZS SETTING correctly it is a 3 lead teater and iam not sure if the earth and neutral have to be linked and what setting it has to be on.
 
Not too sure but i seem to remember that the process is as follows:

Set the selector switch to Zs and connect each appropriate lead separately to Line, Neutral and Earth.
Press Test: depending on the setting the result will be either PEFC or PSC (or if earth disconnected Ze) press F1 to toggle between them.
 
The 9083P will only allow the Earth Loop Impedance test to be performed if the correct voltages are detected between phase-neutral (PN illuminated), phase-earth (PE illuminated) and neutral-earth (NE not illuminated).
Rotate the rotary switch until the Zs test is selected. Press the function key F1 to select either the Earth Loop Impedance test (L-PE) or the Line Impedance test (L-N).
The secondary display will automatically show the appropriate icon: PFC when L-PE is selected and PSC when L-N is selected.
Note: When the Zs switch position is selected, the 9083P will default to the last used setting, even if it has been switched off.
To begin the test, press and release the TEST key.
Note: The 9083P will determine the fault voltage that may appear on the protective conductor during the test. If the fault voltage is greater than 25V the 9083P will indicate >25V on the LCD, but the user may proceed with the test. If the fault voltage is great than 50V, this is indicated on the LCD and the test is inhibited.
 
Last edited by a moderator:
Thanks for the info.In the guide that comes with the tester it does not tell you if the leads have got to be connected ie it shows 3 leads in the diagram and does not give any info some testers as you will know have to have the leads connected when carrying out certain tests. Iam hoping that their is a member who has the same tester who will have the answer I phoned Di log and they was not that helpfull any way thanks for the reply
 

Reply to problem using di log tester 9083P in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
885

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
264
also check you don't have a bad cable are they poe or just running from a normal power supply from the wall
Replies
3
Views
636

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top