Wahzy

Hi guys.

At a job today where 6 low voltage recessed downlights with individual transformers (jcc) have stopped working. Dimmer switch seemed to function as supply at light fittings present. Looked like all 6 transformers have blown. Replaced one and turned dimmer on. Light came on and then transformer blows. Dimmer also blown now.

Changed dimmer for for a switch and tried another transformer. This time it works. Is this just a case of a faulty dimmer that blew all 6 transformers?

fimmer is an Aurora 400W
 
You need drivers not transformers and some dimmers are incompatible with the above.

I dont think the OP mentioned LED downlights so transformers would be fine.

Where they all fed from one junction box or individually looped? What was the voltage, was it particulary high? Have to agree it does sound like the dimmer, perhaps poor connections in the original dimmer?
 
Checked all fittings looped wiring with 3/4 wires at one with feed etc. transformers are dimmable. They are MR16 lamps in fire rated enclosures. Might downgrade lamps to 35w?
 
What rating is the dimmer , if you have 6 x 50W lamps , thats 300watt and theres also the transformers and start up , so if you have a 250 watt dimmer this could have become damaged over time , and may have caused the fault that you have , If you are replacing the dimmer install a suitably rated one ..
 
What rating is the dimmer , if you have 6 x 50W lamps , thats 300watt and theres also the transformers and start up , so if you have a 250 watt dimmer this could have become damaged over time , and may have caused the fault that you have , If you are replacing the dimmer install a suitably rated one ..

The OP said in his first post it was a 400W dimmer.
 
Some electronic transformers specify they'll only operate with a leading edge or trailing edge dimmer.

A word of caution testing the dimmer output, you may get some strange readings because the waveform is modulated and isn't even remotely sine wave in shape some some testers won't give a meaningful or accurate reading.
 

Reply to Problem with x6 down lights with dimmer in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
183
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
Hello What was the conclusion of your problem?
Replies
1
Views
795

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top