I'm at a bit of a loss as to how to proceed.

Had a Ze measured at 0.55 Ohms on a TNCS, contacted DNO who gave a asserted value of 0.52 Ohms. DNO came out and confirmed the result then checked over the earth path to the transformer, worked some magic and came back and measured at 0.44 ohms, they also de-rated the main fuse to 80 Amps from 100 Amps.

All good then? well no, tested today and it's back to 0.55 Ohms. So really wondering how to proceed with EIC.

1, record the result the DNO tested - 0.44 Ohms
2, record my measured result but make a note on the EIC that the DNO is aware of the high Ze.

This is not a test instrument issue as my, another independent spark and the DNO test instrument all tested to within 0.01 Ohms of each other.

This is my second visit, 300 mile round trip, to try to resolve an issue with the DNOs equipment, where do my responsibilities with this end?

The DNO have been contacted again, not sure of what they'll do but if they decide to de-rate the main fuse again we're going to have some serious load issues.

Any thoughts??
 
Last edited:
Yeah I had a rural installation where the ze stipulated on tncs from DNO was 0.5 ohms.
Thankful it wasn't problematic as my zs values where still within tolerances.
It was all rcd protected via 30mA anyway.
 
All this is academic really if all circuits within the installation are 30ma RCD protected, it would have been more relevant in the past before such widespread use of RCDs was regulatory.
It becomes academic if the protective device in the cut out takes longer than 5 seconds to disconnect due to a high ze/zs at the origin.
 
Yes of course but any circuit fault with RCD and MCB protection will disconnect well before the main fuse gets involved.
But if the ze is high when measured at the incoming main switch and above what is required to disconnect the fuse in 5 seconds at the cut out then that's ultimately the issue.
 

Reply to Problematic Ze........ in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
391
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
975
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks I re tested this morning as I had other bits to finish off . I tested three times and it was 0.30 every time . It may have been my leads...
Replies
7
Views
2K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top