For anyone that might be interested or is curious to know the differences in functionality being employed out there - Technology Overview
Last edited:
unfortunately that means the installation is unlikely to be compliant with the flicker regulations, and it's likely to also impact others on the same phase.Installed Immersun the other week customer complaining that all the lights flicker when immersun is being used. Apparently one of the side effects of this device.
because I pointed out 7-8 months ago that it was none compliant, and after a bit of head scratching they said they'd have to work on a fix for it - this was after we'd originally reported an issue last Autumn and been assured it wasn't a problem.Really? And why have they changed their technology??
Installed Immersun the other week customer complaining that all the lights flicker when immersun is being used. Apparently one of the side effects of this device.
yes - well roughly speaking, IIRC the limit is 0.7V fluctuation, so 3 x 0.25V = 0.75V, which is why I said less than 0.25V per kW.Earlier this year an Immersun was measured against the flicker spec and failed by a margin of 4.5 on a long term (2 hrs) test and 6.7 in short term (10mins). Does your 0.25V allow for this?
My house has a 0.7V drop per kW and a different burst fire device I tried induced a lot of flicker. The few people I personally know who have tried burst fire devices of home built origin have all had flicker with 2 resulting in complaints from neighbours.
A statement from Greenologic has just been officially released so I am now allowed to distribute this document that might also be of interest
Gavin
Plenty of others narked with them too for selling so many of their dubious units when there are better products available. There are some phase controlled units that are well filtered so are compliant despite what some may claim here. Greenologic http://www.greenologic.co.uk/SharedFiles/Download.aspx?pageid=176&mid=258&fileid=90 state that with filtering it is possible. Mind you there are other phase controlled products that have little/no filtering and so should not be sold. One I have seen has no more than one small snubber capacitor on its output to provide filtering. Useless.
I would have thought the majority of houses have too much impedance to use an Immersun on although suspect that many are close enough that no one notices the flicker unless it is pointed out to them, even though technically there is more flicker than allowed. What proportion of houses do you think it is not legal in? Lots of posts here about Immersun and flicker and they have never tried to defend themselves as far as I can see because it is indefensible.
I wonder if that buzzing MCB was one of the ones that should have been recalled a couple of years ago but was still installed. I forget the details but a major supplier recalled a large batch of them.
One thing Greenologic do not mention is PWM also gives out considerable EMI. But it is of such a high frequency that it can be suppressed by screening the cable between the controller and the immersion. That is added expense and imagine having to recable a long route to the immersion with screened cables. At least that is what the EMMA people have found I believe on their PWM system. It is all adding up to quite an expensive solution???