pro's advice needed | on ElectriciansForums

Discuss pro's advice needed in the UK Electrical Forum area at ElectriciansForums.net

D

daiplayer

Working in a house , have already rewired the kitchen , have been ok'd to rewire first floor lighting .( due to poor condition)

Am trying to keep costs down for customer when bringing house wiring up to standard.

Will be doing some more remedial works but am trying to suss out whether they need bonding upgrade.

Its a TT with a Ze of 207 , ( high i know ) what can i do about this ? inform dno :- convert to TNC-S?

Any way : PEFC : 1.11 a , ( LOW ) PSCC 1.2KA . HIGHEST Zs in house 3.43 , existing bonding 6mm .

As a rule of thumb ive heard of people using 0.5 of main supply tails : 16mm .

However if i inform the DNO of the high Ze and they convert to TNC-S , pefc will rise to eg: 230/0.35 : 657A min.

Any ideas ? or can show me how to do the adiabatic with this ?
 
The DNO will not care about your Ze value. That's your problem! But 207ohms isn't a hanging offence.
What's the protection for the installation. 30mA rcds on all circuits, or what?

I agree best to ask for PME but you'll probably have to wait for some weeks.

re
ny ideas ? or can show me how to do the adiabatic with this ?

Don't understand, what are you tring to calculate, the size of the earthing conductor?
 
Going deeper will without doubt get you a better reading, more importantly it will be morelikely to be stable. TN levels are achievable but you need a bit more work to get them,
Go for the thickest couplable rods you can get your hands on mate
 
The 6mm earth and 6mm bonding will most likely be fine if the installation is left TT

Indeed, the most it is going to carry is 30mA! That allows your Ze to be as high as 1666ohms (not recommended).

Re adding a rod: If you go that route it will need to be at a distance away at least 3 times the length of the existing rod - there's some interesting papers on the 'net' if you can be bothered. Including here http://www.electriciansforums.net/e...electrical-forum/42851-earth-rod-spacing.html
As stated above, it's better to bang in two new chunky rods coupled together. Doesn't work if you are sitting on a lump of granite, however!
 
your main earthing conductor on a TT system is fine at 6mm as long as it's not buried unprotected. as previous posts, go for a longer rod, at least 1m from the biulding.
 

Reply to pro's advice needed in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top