Working in a house , have already rewired the kitchen , have been ok'd to rewire first floor lighting .( due to poor condition)
Am trying to keep costs down for customer when bringing house wiring up to standard.
Will be doing some more remedial works but am trying to suss out whether they need bonding upgrade.
Its a TT with a Ze of 207 , ( high i know ) what can i do about this ? inform dno :- convert to TNC-S?
Any way : PEFC : 1.11 a , ( LOW ) PSCC 1.2KA . HIGHEST Zs in house 3.43 , existing bonding 6mm .
As a rule of thumb ive heard of people using 0.5 of main supply tails : 16mm .
However if i inform the DNO of the high Ze and they convert to TNC-S , pefc will rise to eg: 230/0.35 : 657A min.
Any ideas ? or can show me how to do the adiabatic with this ?
Am trying to keep costs down for customer when bringing house wiring up to standard.
Will be doing some more remedial works but am trying to suss out whether they need bonding upgrade.
Its a TT with a Ze of 207 , ( high i know ) what can i do about this ? inform dno :- convert to TNC-S?
Any way : PEFC : 1.11 a , ( LOW ) PSCC 1.2KA . HIGHEST Zs in house 3.43 , existing bonding 6mm .
As a rule of thumb ive heard of people using 0.5 of main supply tails : 16mm .
However if i inform the DNO of the high Ze and they convert to TNC-S , pefc will rise to eg: 230/0.35 : 657A min.
Any ideas ? or can show me how to do the adiabatic with this ?