Hi all,
Do I really need 16mm SWA to supply an external garage with a 63A 16A Power 6A Lighting unit? Maximum demand would be 100% of 16 + 40% of 6 which = 18.4 rounded to 19. Current carrying capacity of 16mm is 64A although its like ÂŁ7pm. Or am I getting confused. Should I be saying that the maximum demand is 63A?
It's a TT installation which will have the garage distribution circuit protected by a 32A MCB and then downstream the 63A breaker in the garage has a 30ma RCD protecting the sockets. Upstream there will be a 100ma Time Delayed RCD which will be fitted inside the consumer unit, making the RCD the main switch.
Do I really need 16mm SWA to supply an external garage with a 63A 16A Power 6A Lighting unit? Maximum demand would be 100% of 16 + 40% of 6 which = 18.4 rounded to 19. Current carrying capacity of 16mm is 64A although its like ÂŁ7pm. Or am I getting confused. Should I be saying that the maximum demand is 63A?
It's a TT installation which will have the garage distribution circuit protected by a 32A MCB and then downstream the 63A breaker in the garage has a 30ma RCD protecting the sockets. Upstream there will be a 100ma Time Delayed RCD which will be fitted inside the consumer unit, making the RCD the main switch.