Can anyone give me a few examples of what parallel earths might be there? Thanks. Got the theory, need the practice ......

Yes, any bonding/supplementary bonding, along with simple cpc connections to items that are bonded by virtue of pipework connections (boilers etc.) right down to luminaires sitting in a conductive ceiling grid.
In all but the most basic 'all-insulated' installations, there are many parallel paths.
 
I've seen everything from a tick, N/A, LIM or a back calculated value...
 
Hi Guys and Dolls
In my 2004 edition of the IEE Inspection and Testing Guidance Note 3, page 78, Protective conductor continuity can be confirmed with an Earth fault loop impedence test (R1 + R2 or R2 is not required to be measured). (Note 4)
Ring circuit continuity also does not have to be measured 'Where there are proper records of previous tests and no changes have been made to the ring final circuit'

Is this still allowable under the latest regime for PIRs?
If so, do you rely on a Zs test only?

Pete :winkiss:

Page 73-74 GN3 5th ed. Cost £25. ------:happy:
 
Apologies for ressurrecting old thread
Yes, the 'back calculation' (R1+R2) = Zs-Ze is distorted by parallel earth paths and should not be used.

What if doing an inspection (on empty house) and you disconnected main protective bonds and did Zs -would your Zs - Ze = R1+R2?

Seems a lot of hassle when working by yourself to be doing R1+R2 and a Zs at every point when the results don't really show anything new?
(not got access to a GN3 5th ed) Any thoughts?
 
Apologies for ressurrecting old thread


What if doing an inspection (on empty house) and you disconnected main protective bonds and did Zs -would your Zs - Ze = R1+R2?

Seems a lot of hassle when working by yourself to be doing R1+R2 and a Zs at every point when the results don't really show anything new?
(not got access to a GN3 5th ed) Any thoughts?

Test from furthest point on EICR...
 

Reply to Protective Conductors Continuity in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
642
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
961

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
791

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top