Can anyone give me a few examples of what parallel earths might be there? Thanks. Got the theory, need the practice ......

Yes, any bonding/supplementary bonding, along with simple cpc connections to items that are bonded by virtue of pipework connections (boilers etc.) right down to luminaires sitting in a conductive ceiling grid.
In all but the most basic 'all-insulated' installations, there are many parallel paths.
 
I've seen everything from a tick, N/A, LIM or a back calculated value...
 
Hi Guys and Dolls
In my 2004 edition of the IEE Inspection and Testing Guidance Note 3, page 78, Protective conductor continuity can be confirmed with an Earth fault loop impedence test (R1 + R2 or R2 is not required to be measured). (Note 4)
Ring circuit continuity also does not have to be measured 'Where there are proper records of previous tests and no changes have been made to the ring final circuit'

Is this still allowable under the latest regime for PIRs?
If so, do you rely on a Zs test only?

Pete :winkiss:

Page 73-74 GN3 5th ed. Cost £25. ------:happy:
 
Apologies for ressurrecting old thread
Yes, the 'back calculation' (R1+R2) = Zs-Ze is distorted by parallel earth paths and should not be used.

What if doing an inspection (on empty house) and you disconnected main protective bonds and did Zs -would your Zs - Ze = R1+R2?

Seems a lot of hassle when working by yourself to be doing R1+R2 and a Zs at every point when the results don't really show anything new?
(not got access to a GN3 5th ed) Any thoughts?
 
Apologies for ressurrecting old thread


What if doing an inspection (on empty house) and you disconnected main protective bonds and did Zs -would your Zs - Ze = R1+R2?

Seems a lot of hassle when working by yourself to be doing R1+R2 and a Zs at every point when the results don't really show anything new?
(not got access to a GN3 5th ed) Any thoughts?

Test from furthest point on EICR...
 
What if doing an inspection (on empty house) and you disconnected main protective bonds and did Zs -would your Zs - Ze = R1+R2?

No, because you wouldn't energise the installation with the main protective bonding disconnected.
 

Reply to the thread, titled "Protective Conductors Continuity" which is posted in Periodic Inspection Reporting & Certification on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top