Sly
:confused:
Hi Gents
What should I write down to this box on certificate?
:confused:
Yes ADS or EEBAD
Presence of Earthing conductor, CPC, PDC,Sup's if req'd, etc etc
But not all the installations we work on are 17th edition compliant, so the use of EEBADS is still justified IMO
Sure. But the OP stated certificate not report, so I can only guess that it isn't a periodic for this reason and is therefore some kind of installation certificate. Therefore it must be installed to the 17th (unless it was designed to the 16th - I doubt it) so would have to be ADS, no?
With respect, if the main bonds etc are say 6mm eg 15th edition, then they are adequate but do not conform to current regulations. Therefore I would say EEBADS is appropriate.
My opinion may differ from others.
I was going to come back with a counter argument, but I've been there before on this forum and I can't be a**ed tonight!
Let's agree to disagree!! :)
Reply to Protective measures for fault protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thank you. I think I understand now.