Pscc and Pefc | on ElectriciansForums

Discuss Pscc and Pefc in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Bsharp

-
Joined
Feb 15, 2011
Messages
104
Reaction score
23
Can anybody give me the definitive answer to the question of why on TNCS earring arrangement when testing Pefc and Pssc sometimes the values are different? When we are essentially testing down the same path as the earth conductor and neutral are combined? And therefore both share the same parallel paths etc.
 
Last edited by a moderator:
Can anybody give me the definitive answer to the question of why on TNCS earring arrangement when testing Pefc and Pssc sometimes the values are different? When we are essentially testing down the same path as the earth conductor and neutral are combined? And therefore both share the same parallel paths etc.
Think of the supply cable, it shares a characteristic with T&E in so much as the CPC strands of either the PEN/CNE cable can be of a lower CSA than that of the line conductor, same can be said about the tails.
 
Think of the supply cable, it shares a characteristic with T&E in so much as the CPC strands of either the PEN/CNE cable can be of a lower CSA than that of the line conductor, same can be said about the tails.
Yes I understand the difference in size of the conductors but if the earth and neutral are combined I.e. connected in the cut out then surely the only difference is the size of the earthing tails conductor which at a length of say max 3m’s should be negligible.
So line to earth (CNE)
Or line to live (CNE)
Share the same path?
this is where I get a little confused.
 
It's easier to compare the the Ze and the impedance of the return path from phase to neutral (which on my MFT you have to do first anyway) and see whether the csa difference reasonably accounts for it.

Mathematically, a difference of 0.01 ohms between the two makes a much bigger difference to the calculated PEFC and PSCC.
To get the idea do 230/0.05 and 230/0.06 and see the difference 0.01 ohm makes.
 
It's easier to compare the the Ze and the impedance of the return path from phase to neutral (which on my MFT you have to do first anyway) and see whether the csa difference reasonably accounts for it.

Mathematically, a difference of 0.01 ohms between the two makes a much bigger difference to the calculated PEFC and PSCC.
To get the idea do 230/0.05 and 230/0.06 and see the difference 0.01 ohm makes.y

makes sense now thanks for the replies.
 

Reply to Pscc and Pefc in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
I am living in the north of Thailand outside of the big city. That means in the rainy season we have multiple times per week power outages...
Replies
0
Views
431

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top