acat

TNCS system am I mad went to a house today PME system PSCC and PEFC are supposed to be the same got 4.8kA at main switch and when I did the PEFC I got 7.1kA is this correct and if not what would cause it.

Thanks in advance.



Chris

Sorted just tried the same tests at home looks like my meter may need to go into early retirement
 
Last edited by a moderator:
Megger 1552 readings at home are all over the place as well one minute its 5.1kA kick the dog and cat go back test again and its 7.5kA. Pets know whats coming they run off I go back and check and its back to 5.1kA.

Uo/Ze gives me 7.6Ka


Chris

PS 10volts on meter battery check
 
TNCS system am I mad went to a house today PME system PSCC and PEFC are supposed to be the same got 4.8kA at main switch and when I did the PEFC I got 7.1kA is this correct and if not what would cause it.

Thanks in advance.



Chris

Sorted just tried the same tests at home looks like my meter may need to go into early retirement

was the earthing conductor connected when you did the pscc? if not if not the test would not have included parr earth paths but pefc would which could increase the ka reading
 
Were you using the standard Megger croc clips? I've found these a bit iffy when testing - they quite often need a good squeeze onto the cables to make a good connection.
 
I have very limited experiance but I thought pssc and pefc are usually different by how much I don't lmow but usually I find one to be about 0.34ka and one to be about 0.36ka but this is at my training college so not sure about reall world.

And you just record the higest one as your PFC I belive?.
 

Reply to Pscc = pefc ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
It might be ok
Replies
6
Views
559

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top