Lazenby had a bloody big FRY
 
Aye, thought she'd be up for a bit of Turkish Delight with her sausage and scrambled.
 
dead test R1+Rn. then PSCC= 230V/( R1+Rn).

I can't see how that will work, IMO, as the OP will need access to the front end of the cct. So its a guesstimate.

Since you'll need Zline ext. + R1 +Rn of the sub-main and as the OP doesn't have access to either then its going to be a calculated value based on assumptions about the supply cable type, size, length and the same for the sub-main cable.

We're not even sure whether the supply earthing arrangement is TN or TT, only that the far end supply is TT'd so we might struggle to get a reasonable supply voltage off and on load and calculate the resistance from the volt drop at the far end....

I'd just go for the 'drive-by' calculation if I was you.

that is:
Guess one + guess two + Variations in terminal resistances through various in line connections = 0.5 Ohms

This calculation is only for advanced users only - not recommended for the barn stormer
 
as OP said he had access to switch fuse supplying his installation, i assumed he wanted the pscc for that point.
 
My suggestion is do the live "no trip" test, or normal one and hope for the best,if it trips knock the door and say can you reset the Rcd please, then resort to other methods....how can you do all the other tests you may need to do at the origin of supply?
 
hi have access to the fused connection unit, that the supply comes from in utility room, but the lovely.... householder would not allow access into main house, must of thought i was an electrician who is also a burglar ho ho, we cant choose are customers, well we have a bit of lee-way. all done now using R1 + Rn method
230/(R1+Rn)

Ok, so R1+ Rn from the utility room to the outside installation which can be measured.
We still have R1 + Rn from the DB to the Sw Fuse, Zline ext plus a bit for terminal resistances.....

Just a few thoughts
 

Reply to pscc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
933

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
513
I don’t see an rcd here. Is it elsewhere, supplying this board? It looks like it’s in a garage… is there excessive moisture getting into...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top