Hi Guys

Issue 1

i am looking at changing the DB's in my friends pub from the old mess that is there are the mo. At the moment it has a existing 3 phase board with 5 submaines in it supply the Toilets, Cellar, Out House, Skittle Alley & Kitchen. When I replace this one where does it leave me with 30mA protection on 1 the submaines that are in 16mm T&E and 2 the circiuts that are off of the boards from the submaines i.e. Toilet circuits etc?

Issue 2

Next to the existing 3 phase board I have about 20 circuits spread across 3 old rewirbe DB's which I am looking to put into a 24way board. Now where does this leave me with 30mA protection? I understand that certain circuits would be advisable to fit RCBO's to showers etc but is it nesassary for the rest seeing that the actual fixed wiring was done pre 17th?


Cheers

Ben
 
To answer both questions. Any work that you undertake has to meet current regs. Therefore any cable that requires RCD protection will require an RCD.

The twin and earth submains only require RCD protection if buried less than 50mm.
 
I would be very wary about introducing rcd protection into the pubs I know as most of them have dodgy looking electrics.

rcbo's is the way to go but only after some testing
 
How does that stop 12 circuits all going in the kitchen then if I put the submains on a RCBO? Surely those circuits were already installed prior to 17th?

It doesn't stop you losing all 12 circuits. If you're doing a board change, any circuits on that board need to be fully tested and RCD protection provided where required.

If the 16mm twin and earth cables aren't buried less than 50mm, they don't need RCD's. Either BS7671 or the OSG would be a good reference for you.
 
Make sure you do a full test before changing dbs. There could be borrowed neutrals and earth leakage on circuits already and by the sounds of it most of the circuits will have to be protected by rcbos so you need to check they all ok first , another option is to rewire sub circuits so they don't nead rcd protection
 
your problem with fitting RCD protection to the sub-main board feeds is that a fault will take out the whole sub. i'd be checking the installation method of those feeds and making a decision based on how they were installed. a risk assessment on the likelyhood of damage by nails/screws/plumbers etc. could give you the argument for not fitting RCD to the feeds. documentation of reasons why is advised.
 
Why would you need to change all the other Memera boards? You only need to concern yourself with the circuits that are directly fed from your new board.

However, if you do RCD protect the submains, ensure there are no earth faults on the circuits that the sub boards supply.
 
Yes working in pubs opens a can of worms there is always a spark at the end of the bar happy to work for a pint and budge in a new socket or light , as I said test it out first it might be all ok so you can fit the new db just don't go in changing the db first without any testing
 
Yes working in pubs opens a can of worms there is always a spark at the end of the bar happy to work for a pint and budge in a new socket or light , as I said test it out first it might be all ok so you can fit the new db just don't go in changing the db first without any testing
your right there, a couple were chatting in my local and he was talking out of his arse.

he didnt understand basic things and his mate awasn't any better lol



pubs have the worst installs i have ever seen.


for example sockets in one room were fed from 4 different sub boards and two of them can only be found because we have done a lot of work there.


one of them is, go through a loft hatch and work your way across loads of crap to get to the other side of the building then dig through the mess to uncover the board
 
Hi Guys

Issue 1

i am looking at changing the DB's in my friends pub from the old mess that is there are the mo. At the moment it has a existing 3 phase board with 5 submaines in it supply the Toilets, Cellar, Out House, Skittle Alley & Kitchen. When I replace this one where does it leave me with 30mA protection on 1 the submaines that are in 16mm T&E and 2 the circiuts that are off of the boards from the submaines i.e. Toilet circuits etc?

Issue 2

Next to the existing 3 phase board I have about 20 circuits spread across 3 old rewirbe DB's which I am looking to put into a 24way board. Now where does this leave me with 30mA protection? I understand that certain circuits would be advisable to fit RCBO's to showers etc but is it nesassary for the rest seeing that the actual fixed wiring was done pre 17th?


Cheers

Ben
Quite simply do not attempt to fit rcbos to the sub mains, you will be opening a can of worms, I suspect as this guy is your mate the job is worthless anyhow, a few pints and a meal I suppose, run run as fast as you can, he won't catch you your the 5 week wonder man.
 
So I either have to re-route the submains if even possible! Or change all the other old Memera 2000 boards or try and find RCBO's, are you kidding me?
Its a pub, power is business vital and unlike a house where half a board or whole board trip is just a mere inconvenience... a pub requires a better design and yes to avoid such scenarios if the sub supply is best rerouted or replaced then be it so + RCBO for individual circuit protection.

We are not kidding you and replacing DB's along with testing the install you should already be aware of this, but this is what happens when the domestic brigade moves on to commercial and industrial while lacking experience- you cannot simply apply the same thinking.

You are upgrading the boards to meet current regulation and in doing so introducing RCD protection, how this is achieved is subject to the circumstances and nature of the installation so in you case, yes! its going to cost a few pennies, tell your mate many will just change it like a domestic set up and be very cheap in comparison but to avoid costly power issues down the line your more expensive option is the best way to go.
 

Reply to Pub DB change in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
773
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
873

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top