Hi all,
Not sure if I've posted this in the right place or not. Just looking for a bit of help please.
I need to move a dist board in a gastro pub/restaurant ready for a new kitchen to be installed. I'll not be involved in the Kitchen install itself but need to make sure I put in a suitable supply and board so its ready to go. This board will also be supplying lighting & small power throughout. So that's a bar, restaurant and 3 B & B rooms upstairs with minimal loads.
Currently on site is a 100amp 3 phase supply at the cut out. Then an 80amp switch fuse for a sub main to the existing dist board around 15metres away, the cable for which I had planned to divert and extend slightly for the new board. I told the kitchen specifier to go easy on electrical cooking appliances and use gas wherever possible. They've come back with mostly gas appliances apart from:
1 x combi/steam oven at 32A 3ph (the main ovens are gas)
1 x pizza oven at 20 3ph
1 x dishwasher at 20 3ph
There are a number of other appliances listed as requiring 13amp supplies (a bit vague I feel) for:
2 x hot cupboard
extractor fan
chillers
cellar cooling
coffee machine
fridges
glass washer
fridges behind the bar
Lighting load throughout building is minimal due to all being LED.
I'm happy with the smaller loads but its those 3 x 3 phase appliances I'm not sure what sort of diversity to consider for them. OSG append 4 suggests 100% full load of largest, then 80% of 2nd, then 60% of remaining for small hotels. Might this be a suitable approach? Am I pushing it with the 80amp sub main fuses?
Any help greatly appreciated. Thanks
Not sure if I've posted this in the right place or not. Just looking for a bit of help please.
I need to move a dist board in a gastro pub/restaurant ready for a new kitchen to be installed. I'll not be involved in the Kitchen install itself but need to make sure I put in a suitable supply and board so its ready to go. This board will also be supplying lighting & small power throughout. So that's a bar, restaurant and 3 B & B rooms upstairs with minimal loads.
Currently on site is a 100amp 3 phase supply at the cut out. Then an 80amp switch fuse for a sub main to the existing dist board around 15metres away, the cable for which I had planned to divert and extend slightly for the new board. I told the kitchen specifier to go easy on electrical cooking appliances and use gas wherever possible. They've come back with mostly gas appliances apart from:
1 x combi/steam oven at 32A 3ph (the main ovens are gas)
1 x pizza oven at 20 3ph
1 x dishwasher at 20 3ph
There are a number of other appliances listed as requiring 13amp supplies (a bit vague I feel) for:
2 x hot cupboard
extractor fan
chillers
cellar cooling
coffee machine
fridges
glass washer
fridges behind the bar
Lighting load throughout building is minimal due to all being LED.
I'm happy with the smaller loads but its those 3 x 3 phase appliances I'm not sure what sort of diversity to consider for them. OSG append 4 suggests 100% full load of largest, then 80% of 2nd, then 60% of remaining for small hotels. Might this be a suitable approach? Am I pushing it with the 80amp sub main fuses?
Any help greatly appreciated. Thanks