Would you attempt to pull 16mm SWA through 150M of existing underground conduit?

A potential job I have taken a look at. I would need to be very sure I could get it through before shelling out ÂŁÂŁÂŁ on that much cable! (- I already advised the Customer it would have made much more sense to install a cable before filling the trench!).

Facts:
-Conduit was laid about 1 year ago. It is 50mm dia corrugated plastic type, laid in 3 sections of 50M. - I have no idea of the quality and continuity of the two joints, but the Customer will ask the contractor who laid it in.
-Conduit ~ 600mm deep through a semi-wooded garden, no special precautions such as gravel layer or warning tapes.
-Laid pretty straight for first ~60M, then takes a gentle curve perhaps 20 foot radius and turns total about 60 degrees before the end.
-String is through already to start proceedings, so I would be investing first in lots of cord, and a damn great length of blue rope.
-150M of 16mm will weigh about 150Kg!
- I also am aware it only takes a little bit of mud to make a nice plug!


Questions:
Termination for cable nose and ways to stop it snagging?
Friction being the enemy, - so Lubrication?
Best way to fix cable to rope?
Will I need a tractor ...??? :eek: (- AKA how hard can you pull safely?)
I haven't seen any longer than 100M from distributors. - Can longer single lengths be got?

Homework:
Ongoing decision as to whether I can get away with 16mm anyhow, but that's work in progress, and not my question here.
 
Use a cable sock, together with a cable pulling machine hired from HSS or Speedy along with the correct cord for cable pulling not polycord and it will go through slowly but surely
 
Me and my old boss tried something similar years ago. Same ducting and cable size. Duct about 80metres long with a slight dogleg at one end. We had to tie the rope to the back of my van as pulling it by hand was impossible. Managed to get it 80% of the way but the rope snapped when the SWA reached the dogleg. we dug a hole found the break and managed to finish the job but to be honest I'd never wanna do it again.

Just let the customer be aware that it might not be possible.
 
Me and my old boss tried something similar years ago. Same ducting and cable size. Duct about 80metres long with a slight dogleg at one end. We had to tie the rope to the back of my van as pulling it by hand was impossible. Managed to get it 80% of the way but the rope snapped when the SWA reached the dogleg. we dug a hole found the break and managed to finish the job but to be honest I'd never wanna do it again.

Just let the customer be aware that it might not be possible.

E54 ain't gonna be pleased with your van antics :lol: Daz
 
OP, There is some sound advice in amongst the absurdities, I would also recommend a Mandrel to test that the ducting is still "true". Running a mandrel of a slightly smaller size than interior of duct will save you a lot of heartache.

Regards

Billy
 
I had a job a few years ago to pull 70m through a 50mm underground conduit. Have to say NEVER AGAIN will I take on that kind of job as even the slightest rise or kink on the conduit can result in the cable sticking, in the end it was a case of digging several holes and and two days locating the conduit before being able to get the new cable plus being out of pocket on the job.
 
"Never again". - That's a recurring theme! I was just talking to the hire company about their winch, and they don't really know how to use it. For instance 10mm polypropylene (~ 1 tonne break, but very stretchy, maybe need to go bigger) or spend an arm and a leg on dyneema rope (winch manufacturers say use non-stretch rope).
 
"Never again". - That's a recurring theme! I was just talking to the hire company about their winch, and they don't really know how to use it. For instance 10mm polypropylene (~ 1 tonne break, but very stretchy, maybe need to go bigger) or spend an arm and a leg on dyneema rope (winch manufacturers say use non-stretch rope).

While I don't know much about pulling very long cables (and I'm going to be very wary if anyone ever asks me to now), why does it matter if the rope is stretchy? Could it be good to have some stretch in it, to reduce the mechanical shocks to the cable? Perhaps E54 or someone can advise.
 

Reply to Pulling 16mm SWA through 150 M of conduit? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

  • Question
Thanks guys, I ran UF-B. Never handled 6/2 before, wasn't as difficult as I expected.
Replies
3
Views
936
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top