How do you guys pull your cables through conduit. What have you found the best method.
im really old school,i use my eyes..tho has anyone noticed even when you use a laser or a level it still looks pisd compared to anything else thats been previously installed,thats when i use the good old fashioned eye to make good.:stuart:
i am replacing a 6mm cable for a 10mm cable this week through an old system of conduit which im assuming is a 25mm diameter but in case it is full up would it be easier to run single core's in instead i'm wondering. which if ive aready bought the twin and earth i can splice the doubled insulation off remove it and use the 3 single insulated if it is already mechanically protected surely?
I would imagine pulling a 10mm t&e through conduit would not be much fun especially if there are other cables already in the tube and/or if there are a lot of bends to pull round. Even with inspection boxes you will struggle with t&e in my opinion. Unless it is a straight run I would definitely use singles. Cant you take the t&e back?
Cheers Andy your a mind reader I was thinking this today. I am going to buy the singles and a length of single 2.5mm2 cpc. I havent bought the T&E yet luckily! Although i supposed it wouldnt do no harm stripping the outer sheath of to use the singles inside if i had of bought it.
No I havent to be honest with you. well what someone has told me is that will be fine. its for a 10.5kw load 50a mcb and 10mm2 conductors.That CPC is a bit near the bone, have you checked if it will be man enough