Had a really weird situation today. Having installed all the wiring and new consumer unit for a full rewire, I today came to test the last circuit which was the downstairs lights. Tested continuity which was fine as was insulation resistance, upon testing for loop impedance, I got a low voltage error message which upon investigation showed only 185 volts between first and 2nd light points. Result was I ended up having to take up the floorboards and replace the cable which looked totally normal and undamaged. Has anyone else had anything like this happen to them?
 
What do you mean exactly by 185V between first and second points. Can you clarify that? Are you saying you had 240V at the first fitting and 185V at the second?
 
Tested continuity which was fine

Did you test both L & N? If not, the N conductor might have been internally broken. the 185V was probably arbitrary and just indicative of a high resistance, if you had used a different meter or put more load on it probably would have changed.
 
If you had 240v across L&N at the first fitting and 185V across L&N at the second fitting I would say you lost the neutral, either the cable had a break or a poor termination.
 
Tested both L and N with no high readings, even did a continuity test on the cable once I have removed and replaced it, again no high readings, that what is so weird.

If you still have that leg of cable put your continuity tester on the neutral at either end, then flex the cable around and see what happens on your scale.
 

Reply to Puzzled in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Very technical :D
    • Like
Replies
9
Views
446
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
357

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top