Hi All

got call out to a domestic fault on consumer unit totally separate from the job & client mentions to me that they had Battery storage fitted to the PV.

anyway they mention that at present they are trying to contact company that installed it as their electric bills have gone up & they don't think it is working correctly & asked me to have a look.

have a look whilst at the property & found that the original system was a 4kw split on two roofs.

PV 3.68kw SMA inverter with two strings
retro fitted Growatt SP2000

now system is one string into original inverter, second string removed & through the SP2000 & back into the SMA.
not working through the MPPT, first inverter now I don't think is operating at any sort of capacity & think most of time is just sitting looking pretty.

so now we have 8 panels trying to charge 5KW battery storage with any spare electric.

anyway speaking with client I have not touched the system & have passed on the RECC & MCS information for complaints.
the other best bit was that they were cold called & two days later & guy was out shiny suit & all, sign up today & we can install in two days.
bang & job done & any guesses to how much ............?

also customer says they installed on my android device the App & set it up & before they left they removed the system from the android device.
labour looks like about 2 hours as all in loft on the wall all to hand. (nothing wrong with that install a bit messy)

customer has had PV for some time as on top tariff, monitored electric bills for some time around £55.00 per month over the last year or so, now at £75.00 per month.
also has heat pump & solar thermal hot water. all electric but no storage heaters. only 2 at home one working.
asked if they thought Battery storage was for them & I said yes if it was installed correctly yes they would be saving a little. showed them 4 kw system with battery storage on my device only few miles away & we were making savings that day.

won't touch the system until she has gone through complaints & am going back later next week to finish of works on domestic system.
will take pictures at that time & post up.

even today we are generating battery power even with a sh.t start to the day now at 34% & climbing
 
Last edited:
SP2000 cannot handle multiple strings with dual MPPT - hence the way this one is fitted.

Need to check that the sensor is fitted the right way round and that the PV output V matches the SP2000 input V and the output V of the SP2000 matches the input V of the inverter.

Check all polarities.
 
Last edited by a moderator:
Hi TedM

seeing it I knew it was not going to work due to MPPT, at present I have advised them to contact installer which they had done before I arrived 3 times with no reply.
they had also gone to citizens advice before I had been & had a look & where advised to write 3 times before further action, since then I have given information for RECC & MCS so they can contact them also.
 
Go on then, the price was .... £6500
 
Forgot the salesman's £500 commission :)
 
I think as we all pointed out earlier (a few months ago) that we are going to see a plethora / rash of problems like this over the next 6 - 9 months, which could well result in a BBC Watchdog / Rogue Traders slot.
 
hi spinlondon

think you just have to inform DNO of the battery storage being installed so they are aware that if they work on the system say during the hours of darkness there could still be power being discharged into the grid.
 
As per thread elsewhere (in the Green Lounge), ALL battery storage systems are considered generators and require DNO notification / approval - see also marc8's recent other thread http://www.electriciansforums.co.uk...nels-forum/108879-pv-battery-storage-mcs.html

My guess is that seeing as these system do not require MCS certification that the sales led organisations are completely ignoring all advice and guidelines from BRE / IET / RECC / MCS et al


BRE Free Consumer Guide: http://www.bre.co.uk/filelibrary/ns...66-BRE_Solar-Consumer-Guide-A4-12pp-JAN16.pdf
IET Code of Practice: Code of Practice for Grid Connected Solar Photovoltaic Systems - The IET
 
sP2000 system has an inverter which has now been added to the system & therefore altering the system ? am i correct ? if so this would come under MCS
 
sP2000 system has an inverter which has now been added to the system & therefore altering the system ? am i correct ? if so this would come under MCS

In a retrofit environment not necessarily. It would be covered by any DNO requirements - ENA / IET Guidelines, Regulations or Codes of Practice, BS7671 and FiT scheme regulations
 
Last edited:
I see

think the system won't work as I think the SMA is only single MPPT same as the SP2000, i will find out when i get back there next weekend & will have more details by then
 
now system is one string into original inverter, second string removed & through the SP2000 & back into the SMA.
not working through the MPPT, first inverter now I don't think is operating at any sort of capacity & think most of time is just sitting looking pretty.

so now we have 8 panels trying to charge 5KW battery storage with any spare electric.
does this return into the 2nd MPPT on the inverter?

If so then it's installed correctly.

Not sure why anyone is talking about DNO notification as nothing has changed, it's still only the SMA inverter connected to the grid, the growatt is connected through the inverter.

customer has had PV for some time as on top tariff, monitored electric bills for some time around £55.00 per month over the last year or so, now at £75.00 per month.
also has heat pump & solar thermal hot water. all electric but no storage heaters. only 2 at home one working.
erm, it's winter, PV does much less in winter, heat pumps will be running a lot more, solar thermal will be doing nowt, and there will be very little spare generation to charge batteries up in winter.

What makes you think that it's odd for the bills to be higher now than the average for last year?
 

Reply to Pv Battery Storage Retro Fit in the Green Energy Forums | Green Energy Hub area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
408
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
996
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

From the front cover of the manual: Newlec Helpline: 0800 783 6909 https://www.manualslib.com/manual/3408290/Newlec-Nlsh050.html#manual I think...
Replies
1
Views
261
Depending on the specific battery you (intend to) buy, you might be able to just do Monster alternator -> LiFePo4 battery. The BMS for the fancy...
Replies
5
Views
367

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top