This afternoon I observed your real-time power figures for Generation, Grid, Battery and Consumption. It has clearly been very sunny where you live because the generation figures have been up in the 5-6kW range. The temperature of the inverter has exceeded 60C and you have had a shutdown of generation.
What I observed was 4600W output from the inverter to the CU; 900W consumption from the CU; 3700W export.
4600 = 900 + 3700.
With such high solar generation the battery should not be being discharged yet it was at a rate of 170W - this is not right. There is ample solar to supply the load and any export.
Here is the wrinkle; your installation is not set up to export because the backflow power is set to +0000W. And yet it is exporting - why?
I reckon the current sensor which monitors the glow of grid power into and out of your home is orientated the wrong way around - they have an arrow to indicate the supply and the CU direction - you could check this easily.
It might be though that the current clamp is orientated the correct way but its leads have been wired into the meter (which relays data to the inverter meter comms socket via an RS485 cable) the wrong way.
The wrong orientation of the current sensor or a switch over of its leads will reverse the sense of the data input on grid power flow so the inverter will interpret an export as an import and an import as an export.
For the self consumption mode of operation, any grid import is offset by the injection of inverter ac power of an amount conditional on the kW limit of the inverter pertaining at the time and the incident sunshine on the panels. The inverter does not use power from the battery for export to the grid - this battery is solely for home use.
A negative feedback loop controller ramps up PV generation until the ac output power cannot be increased any further. As the ac output power increases the imported power should reduce and if there is sufficient pv generation to zero import. However if the sense of the signal is incorrect the imported power signal rises and rises because it is actually representing export of the very same increased pv generation - a positive feedback loop - ie: export power becomes maximised. The inverter starts to get hotter.
When one studies the ac output power plot it cycles between maximums and a minimums in a way determined by the temperature related power output derating scheme, incident sunshine changes and load changes in the home. Eventually the inverter shuts down (or becomes unstable at higher temperature and looses sync with the mains) . It cools down, restarts and then carries on again.
Power figures right now: Gen 3.25kW, Load 0.9kW, Export 2.25kW Battery discharge 0.15kW