davesparks
Hmmm I see.
what would you do? I can't say as I know really.
Install the PV circuit in such a way that it does not require RCD protection as an RCD will not provide protection to the circuit.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Pv on rcd in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Hmmm I see.
what would you do? I can't say as I know really.
Surely having an RCBO on it is going to be better than just having an MCB?
So I would be right in thinking that an RCD won't provide protection to the typical PV circuit you see in domestic installs.
Hmm its food for thought...i think you are right. Do you think (iv) of 551.7.2 should apply?
Lol, why should the PV supply disconnect in the event of a RCD tripping, and how will the PV power bypass the tripped RCD?
So I would be right in thinking that an RCD won't provide protection to the typical PV circuit you see in domestic installs.
That's how I've always understood it. I remember suggesting an RCD at the 'PV' end of the install (assuming that it's cable run required it) on here a few years ago but can't remember what the general consensus was.
That would work would it not?
Why would the PV supply be connected to the load side of an RCD?
PV is a secondary supply and should be connected at or very near to the origin of the installation.
Reply to Pv on rcd in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net