Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

It looks like the Henji panels have an Vmp of around 50V per panel, vs around 36V for the sanyo H series panels.

The voltage of the array relative to the inverters peak operating voltage can make a significant difference in the inverter efficiency - 2-3% sometimes, so for the experiment to be fair the panels should both have been at the same (or very similar) operating voltage.

You may be able to use the inverter's performance data to work out a correction factor to apply to remove the impact of this aspect of the design from the results.
 
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

Well, a salesman told me that when you have potentially shaded conditions, you MUST buy the most expensive panels because they are designed to deal with the shade.

I'd love to ask him to explain why the most expensive panel deals with shade better than a cheaper panel which has more bypass diodes.

In other news, great experiment.

I do think that the trees should be cut back so that you receive zero shade on the roof at all times if you want this to be an accurate experiment.

I'm looking forward to seeing how they get on. My prediction is that the Sanyo panels will come more into their own towards the summer and produce more than the cheaper panels over the year - however, not enough to justify their extra cost.
 
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

Suntech monocrystaline panels are outperforming Sanyo Hits in low light conditions by 10-15%, but underperfoming significantly in bright conditions (40%).

Interesting stuff.

How long has the experiment been going on?

The reason I ask is that low light can also mean that the panels are cooler. In the winter this will put the Sanyo panels at a disadvantage as they work better in warm conditions. I would expect the Sanyo panels to perform better in low light conditions AND bright conditions when the summer rolls in.

Keep us informed of how it goes.
 
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

It looks like the Henji panels have an Vmp of around 50V per panel, vs around 36V for the Sanyo H series panels.

The voltage of the array relative to the inverters peak operating voltage can make a significant difference in the inverter efficiency - 2-3% sometimes, so for the experiment to be fair the panels should both have been at the same (or very similar) operating voltage.

You may be able to use the inverter's performance data to work out a correction factor to apply to remove the impact of this aspect of the design from the results.

Thanks Gavin, you are quite correct. I engineered out much of this potential error by wiring the HJs series-parallel and the Sanyo in straight series. An extract from my as-built spec (volt drop calcs) appears below.

It works out that the Vmp for the HJs is 466V, and the Sanyos 642V. So yes, greater cable losses for the HJ array, disadvantaging the HJs (although only really significant as max power is approached), and possibly different inverter efficiency at these two voltages.

You are right in that this should (at least to some extent) be allowed for in the final verdict. BUT it could also be argued that the voltages chosen by the manufacturers are whatever they are, with a corresponding impact on efficiency in a real world scenario, as this is.

This morning the HJs were running at 388V, and the Sanyos at 549V, which is within a few percent of the theoretical ratio.

Cheers, Mark



ARRAY 1 (HJ)
16No. 250W Hengji Solar HJM250M-3232 panels, wired in two series circuits of 8 panels each, paralleled.

Total current at max power, where panel Imp = 4.94A
4.94 x 2 x 1.25 = 12.35A
Total voltage at max power, where panel Vmp = 50.6V
50.6V x 8 x 1.15 = 466V

Total Isc where panel Isc = 5.35A
5.35 x 2 x 1.25 = 13.4A
Total Voc where panel Voc = 60.5V
60.5 x 8 x 1.15 = 560V

Note the de-rating factors of 25% and 15% are to allow for possibly over-spec panels.

Cable volt drop calculation for the 180m dc run on 10mm 4-core (4.7 mA/V/m):

Vd = 4.7 x 180 x 12.35 / 1000 v = 10.45V

10.45 / 466 x 100% =
2.24%



ARRAY 2 (Sanyo)
16No. 250W Sanyo HIT-H250-E1 panels, wired in a single series circuit of all16 panels.

Total current at max power, where panel Imp = 7.18A
7.18 x 1 x 1.25 = 9.0A
Total voltage at max power, where panel Vmp = 34.9V
34.9V x 16 x 1.15 = 642.2V

Total Isc where panel Isc = 7.74A
7.74 x 1 x 1.25 = 9.68A
Total Voc where panel Voc = 43.1V 4
3.1 x 16 x 1.15 = 793.0V

Cable volt drop calculation for the 180m dc run on 10mm 4-core (4.7 mA/V/m):

Vd = 4.7 x 180 x 9 / 1000 v = 7.614V

7.614 / 642.2 x 100% =
1.19%
 
Last edited:
Last edited:
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

Well what would compliment all this is LIVE feed data going to a website with compounded figures, accurate logs of the weather overhead, relative to spot values and/or a live feed webcam looking at what the panels more or less are facing, as annual mean figures are one thing but it would be also nice to see how both sets of panels react to different levels of light at different times of the day
 
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

BUT it could also be argued that the voltages chosen by the manufacturers are whatever they are, with a corresponding impact on efficiency in a real world scenario, as this is.
you could indeed argue that, but it'd be a flawed argument that'd be pretty easy to shoot down for reasons that really ought to be obvious.
 
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

How about a live interview with a panel to find out how it is feeling being put under this much pressure to perform? :)

Will the panels get randomly drug tested to make sure no ones tempted to use performance enhancing drugs?
 
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

Irrespective of second order effects, I feel that the OP should be applauded for running the test. As has been stated many times on every PV forum, data is only useful under real world conditions and under the same conditions. Placing arrays as you have is about as good as you can sensibly get. I see no issue with shading. Most of us have some. It will be interesting to see how the two panel types behave given the fact that their diode arrangements and bypass zones are totally different. I would like to see some form of dappled shading retained across the whole array as this is far more real world.
 
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

Awesome experiment, very well done. Great for mere mortals such as myself!
 
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

Irrespective of second order effects, I feel that the OP should be applauded for running the test. As has been stated many times on every PV forum, data is only useful under real world conditions and under the same conditions. Placing arrays as you have is about as good as you can sensibly get. I see no issue with shading. Most of us have some. It will be interesting to see how the two panel types behave given the fact that their diode arrangements and bypass zones are totally different. I would like to see some form of dappled shading retained across the whole array as this is far more real world.


Indeed, I agree as in the olden days we had ppl like "WHICH" who use to do tests/comparisons of such nature..........
 
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

At face value, this appears to be a good experiment. If it was meant to be 100% scientific then it would be taking place in a lab! This is being done in the real world, in real life conditions so would be keen to see the results.
Part of the reason I have replied to this thread is so I can stay up to date with it but having tracked down the co-ordinates to somewhere around Tibenham, I am only about 6 miles away so the data would be very interesting from a local, personal point of view.
 
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

I am currently monitoring 2 systems: Suntech v Sanyo Hits

Suntech monocrystaline panels are outperforming Sanyo Hits in low light conditions by 10-15%, but underperfoming significantly in bright conditions (40%).

After a "Burn in Period" The Suntech 250W are now performing better in low light conditions and very close to the efficiency of the Sanyo HITS in bright light conditions.

Moral of this story? Sanyo HITS are far more expensive, but dont outperform as much as they need to, to justify their economic outlay.
The Sanyo Hit panels are currently outperforming the monocrystalline Suntechs by 4-5%. They cost a 40-55% premium.
 
Last edited:
Re: PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world t

After a "Burn in Period" The Suntech 250W are now performing better in low light conditions and very close to the efficiency of the Sanyo HITS in bright light conditions.

Moral of this story? Sanyo HITS are far more expensive, but dont outperform as much as they need to, to justify their economic outlay.
The Sanyo Hit panels are currently outperforming the monocrystalline Suntechs by 4-5%. They cost a 40-55% premium.

To be totally honest, I am a fan of Suntech panels but this just isn't good science. The Suntech panels are fitted at a better pitch (30 degrees) than the Sanyo system (45 degrees) and we know very little else about the systems.

The data suggests that both systems are south facing and unshaded - now we all know that if they are going by SAP calculations then zero shading doesn't exactly mean just that. We don't know how the inverters are mounted, how far the cable run is or pretty much anything else about it.
 

Reply to PV Panel War: Sanyo v. Hengji. The ultimate side-by-side long-term, real-world test. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top