R
richsogecko
Hi,
Quick compliance question regarding the AC aspect of a PV circuit...
Imagine a standard domestic <4kWp install on a 3 storey town house. Because of the geography of the house and the internal decoration there's no way to run a dedicated circuit back to the main board.
The alternative would be to sacrifice a top floor socket outlet in favour of a 2W garage board and connect the PV into a 16A MCB within the garage board (along with rotary iso and gen meter)
So protection would be 30mA RCD on main board, 32A Type B on Ring Circuit, 30mA RCD on Garage Board, 16A MCB for PV circuit.
Notwithstanding that a) there is no way to discriminate between 30mA RCDs in series (albeit the Garage board one is only protecting the upstream PV circuit) and b) the Guide to PV would 'preferably' want a dedicated circuit to the main board, is there anything technically not compliant with this method of installation.
We're confident it meets the guide (or doesn't contravene) but a second opinion is always welcome...
Quick compliance question regarding the AC aspect of a PV circuit...
Imagine a standard domestic <4kWp install on a 3 storey town house. Because of the geography of the house and the internal decoration there's no way to run a dedicated circuit back to the main board.
The alternative would be to sacrifice a top floor socket outlet in favour of a 2W garage board and connect the PV into a 16A MCB within the garage board (along with rotary iso and gen meter)
So protection would be 30mA RCD on main board, 32A Type B on Ring Circuit, 30mA RCD on Garage Board, 16A MCB for PV circuit.
Notwithstanding that a) there is no way to discriminate between 30mA RCDs in series (albeit the Garage board one is only protecting the upstream PV circuit) and b) the Guide to PV would 'preferably' want a dedicated circuit to the main board, is there anything technically not compliant with this method of installation.
We're confident it meets the guide (or doesn't contravene) but a second opinion is always welcome...