S

sl1210

Went to a job in a church hall today where one of the power circuits was tripping the rcd. There seems to be 4 bad legs of pyro in the circuit, as I get a dead short in my IR tests between line/neutral, line/earth.

Is it common for pyro cable to do this after a certain time, or could a fault have caused this?

I have disconnected all the faulty legs and managed to keep the rcd on with only one socket working. I'm going to have to re-link the damaged pyro with new cable.

Was wandering if I could use 2.5mm FP cable clipped direct, or whether because its a church hall i would need to run it in plastic conduit???

Cheers
 
I find it strange that four lengths of Pyro have gone down at the same time and can't help but feel the OP's lack of any useful experience with Pyro is not helping in identifying the problem or it's cause

It would be interesting to have sight of the last PIR / EICR to check the IR values of the circuit in question when it was last tested
 
church walls are mostly solid rather than cavity and as such are virtually permanently damp , so i'd go with water ingress at a possibly hidden j.b's / counduit boxes somewhere.
 
i would have thought dampness at first read too but if the ends were made of correctly and have been there for years i would suspect either there has been someone that knows nothing about pyro turning the pot after its been made off or some other damage else where but find it very strange that 4 cables go all at one time.
 
hi guys. like i said i can trace the pyro from the first socket to a metal conduit box on the other side of the wall of the consumer unit, where it then joins singles in a connector and then to the consumer unit.

so my readings cant be because of a connected load as i had separated all the cables.

like i said as soon as i plugged my make shift extension lead into the suspect pyro's they trip instantly. only a couple held.
 
when i disconnect the piro from the connector block with singles going to the consumer unit the rcd holds. as soon as i touch the piro line to the single line. rcd trips.

i'm sure its damp too but really wouldn't know how to dry it. and i'm sure it could happen again anyways
 

Reply to Pyro Cable Tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
948

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
389
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top