Changed a consumer unit today, Advised customer on PIR first but to no avail, so i changed the old consumer unit for a 17th edition dual rcd one, All circuits fine apart from the lighting circuit which trips instantly, Did the standard tests and found allsorts of problems with the neutrals and earths throughout the circuit , Now the problem i have is the entire installation is Pyro , Theirs no loft or floorboards ( second floor flat) so i have no minimal access to cabling, Advised the customer the lighting circuit needs rewiring, But they dont want to go for it and keep explaining to me " It worked before" ( May i also add the customer is polish!!) Now as a temporary measure until i get back their next week ive put the lighting circuit on the mainswitch side of the consumer unit , to atleast give the tenant lighting, Can anybody advise me on the best way to go about this as this work has to be certificated and i dont want to put my name anywere near this lighting circuit !

Many thanks
 
As i see it, you need to progress a testing exercise through the circuit, marking and inspecting each core as you go. As others have stated this sounds more like something has been disturbed, a pinched cable, or a previously damaged sleeve that's now allowing the conductor to come into contact with something. It's a bummer i know, but it needs to be fixed at the end of the day.... lol!!
 
All sorts of problems throughout with neitrals and earths will in all probability be one or perhaps two sections.it can and should be traced with little effort and they can decide on remedial action if agreed

As far as doing tests prior to a consumer unit change,its each to his own,I personally do nothing other than a cursory glance at the installation,but with the attitude that if something is amiss,I will sort it

If there has been no disturbance to the pyro pots.it probable its not cable faults,rather poor connecting or faulty fittins
It seems to be you took the job on and should try and pin down where the faults are arising,rectifying those faults is a different matter
With the required work needed to put it right explained to the customer.its their decision.if they dont agree to problem sorting, then you have done all that could be reasonably expected
Leave it with overcurrent protection and note the problem on the Eic and get paid
 
[ElectriciansForums.net] Pyro Help Please
Welshsparky i was not giving you a hard time but I have come across this once to often 90% of the time for burglar alarms and the rest for door entry systems and I have seen one on a RCD board where the guy did it as a stop gap and never went back and that was 4 years ago
 
Surely this is precisely the reason an EICR needs to be done beforehand? If it were optional very few customers would go for it (or at least pay for it), after all there doesn't seem much point testing an old CU which is going to be changed straight after anyway.
 
after all there doesn't seem much point testing an old CU which is going to be changed straight after anyway.

True, but this should not stop some basic checks such as IR L+N-E, Ze, and checking for borrowed neutrals etc., how in depth you check depends on the condition and age of the installation, how much DIY bodgery has been done and so on before carrying out a CU change, this is in my own interests.

I rarely carry out a full blown EICR or full I&T because as you say, most clients would not pay for it, but I always test as much (or as little) as I think I need beforehand at the survey stage, as mostly these installations did not have RCD protection before the CU change, and I don't like nasty suprises, Besides some of the test results may not change and can go on the EIC.

I also explain, before the change, that any faults found will need to be rectified at further costs to the client.
 
I've the learnt the hard way, as many others probably have. Test before installing, even basic tests will give you and idea if the new CU will function properly without any remedial work. You can then advise the customer that there are problems that need sorting and not try to argue the point after the new CU is fitted.

In the grand scheme of things a few basic tests can save hours of headaches and arguments.
 
you are saying trhat you are leaving the lighting curcuit non-rcd protected. it's no less safe than before, but cover your arse and make sure it's noted on the EIC as a fault that the customer refuses to pay for rectification.

There is no requirement to RCD protect a lighting circuit wired in MIMS cable.
 
True, but this should not stop some basic checks such as IR L+N-E, Ze, and checking for borrowed neutrals etc., how in depth you check depends on the condition and age of the installation, how much DIY bodgery has been done and so on before carrying out a CU change, this is in my own interests.

I rarely carry out a full blown EICR or full I&T because as you say, most clients would not pay for it, but I always test as much (or as little) as I think I need beforehand at the survey stage, as mostly these installations did not have RCD protection before the CU change, and I don't like nasty suprises, Besides some of the test results may not change and can go on the EIC.

I also explain, before the change, that any faults found will need to be rectified at further costs to the client.
I meant from the customer's point of view. You should carry out the relevant inspections and tests before changing the CU to identify these problems and deal with and charge accordingly.
 
We had this discussion when I did the 2382 - MI may have an earthed sheath but it still isn't capable of withstanding penetration by a screw or nail or suchlike.

It doesn't have to withstand penetration from a screw/nail, the same as T + E can not withstand penetration.

MICC cable is BS 60702-1 and therefore comes under regulation 522.6.100 with regard to being buried less than 50mm, and so does not need RCD protection.

But regardless of that, if there is a fault then it should be found. If it is a case of borrowed neutrals etc then stick it on an MCB.
 

Reply to Pyro Help Please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
768
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top