Hello Does anyone know how to program the PGM output to be on when the alarm is set. I want to use it to drive a relay to stop a roller shutter door opening when the alarm is set. software is V09.53d
Thanks
Thanks
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Pyronix Enforcer PGM output in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
Thanks I'll have a lookIt is indeed under change outputs in the installer menu
Not done it on these but I'd assume its in the "Change Outputs" option of the engineer menu?
Just Got round to trying it and i can not get 12v output. So in "Endstation Outputs" i have set PGM to 22(Final set any). Wired the output to PGM1 and COM on the next terminal block Z33, COM,+12V,Z34It is indeed under change outputs in the installer menu
Thanks that would explain it. But the PGM1 output is just a single terminal so I don't know how to wire through it.The output doesn't provide 12v it will just be a switched relay going from NO to NC on final set.
If you need 12v on final set then maybe try wiring from the 12v positive straight the the relay and then wiring a negative from the negative terminal and through the output then to the relay. This way you will get your 12v on final set.
It is indeed under change outputs in the installer menu
Not that I can find. The only output i can see is PGM1Are there not NC/C/NO terminals?
Would you be able to put up a pic of the panel and we will see of we can help you from there?Not that I can find. The only output i can see is PGM1
Sorry For the late reply i missed it.Would you be able to put up a pic of the panel and we will see of we can help you from there?